FUNCTION_BLOCK CNCT
This function block establishes a Profinet DeviceAccess-AR or a Profibus-DPV2 connection.
Supervisors need this connections to access a Field Device, e.g. for writing parameters.
One instance of a CNCT function block provides one instance of a peer-to-peer connection to a Field Device. Only one connection to the same Field Device can be established.
A connection is established when the REQ input is equal to TRUE. The IO Subsystem remains connected as long as the function block is called with REQ = TRUE or an error is indicated.
The variable given D_ADDR input shall identify the destination Field Device. The ID output identifies the established connection to this Field Device (used for the functions blocks RDREC and WRREC.
If the connection is established successfully, the VALID output indicates that the connection can be used.
Note
In case of inactivity, which means there are no read-/write-services transfered on the established connection, the connection may be aborted by the IO subsystem (e.g. after 20 sec.)
Note
The CNCT function block defines a connection to a slot or subslot of a Field Device and returns a handle via the ID output. This connection establishes an Application Relationship (AR) to the Field Device. If another connection and handle is needed to the same Field Device the existing AR may be used.
Code-Example: establish a Supervisor connection
PROGRAM PLC_PRG
VAR
cnct : CommFB.CNCT;
startConnect : BOOL; //establish a Supervisor connection
rdrec : CommFB.RDREC;
loadData : BOOL;
buffer : ARRAY[0..255] OF BYTE;
END_VAR
cnct.D_ADDR.SYSTEM := CommfB.IO_SYSTEM_TYPE.PROFINET_IO;
cnct.D_ADDR.PN.D.STATIONNAME := 'pnDevice';
cnct.D_ADDR.PN.D.VENDOR := 16#011D; //get this data from GSDML or DCP_Identify / Scan
cnct.D_ADDR.PN.D.DEVICE := 16#02EE;
cnct.D_ADDR.PN.D.INSTANCE := 0;
cnct.D_ADDR.PN.SLOT := 0;
cnct.D_ADDR.PN.SUBSLOT := 1;
cnct.REQ := startConnect;
cnct();
IF(cnct.VALID) THEN
loadData := TRUE;
ELSIF(cnct.ERROR) THEN
//re-connect, if connection timed out
startConnect := (cnct.STATUS = CommFB.ErrorCode.TIMEOUT);
END_IF
// Read Diagnosis-Data
rdrec.REQ := loadData;
rdrec.ID := cnct.ID;
rdrec.INDEX := TO_INT(ProfinetCommon.DiagnosisRecordIndex.Device);
rdrec.MLEN := TO_INT(SIZEOF(buffer));
rdrec.RECORD := ADR(buffer);
rdrec();
IF(rdrec.REQ) THEN
IF(rdrec.VALID) THEN
loadData := FALSE;
startConnect := FALSE; //Release connection
END_IF
END_IF
rdrec.REQ := rdrec.BUSY;
InOut:
|
Scope |
Name |
Type |
Initial |
Comment |
|
Input |
REQ |
BOOL |
Start Request |
|
|
D_ADDR |
Data structure to define the address of a slot of a PROFIBUS DP-slave or a subslot of a PROFINET IO Device |
|||
|
Output |
VALID |
BOOL |
Connection is valid |
|
|
ERROR |
BOOL |
Error detected |
||
|
BUSY |
BOOL |
FB is busy |
||
|
STATUS |
DWORD |
Last detected status |
||
|
ID |
DWORD |
Constants.INVALID_ID |
Identifier of a PROFIBUS DP-slave or a subslot of a PROFINET IO Device. Use for RDREC or WRREC (Class 2 / Supervisor Access) |