TM5CSLCx00FS Safety Logic Controller
Group: Basic
Parameter: CycleTime
|
Default value |
2,000 |
|
Value range Step size |
2,000...20,000 1 |
|
Unit |
µs |
|
Description |
Sets the cycle time of the Safety Logic Controller. |
|
Possible values |
The parameter value 'CycleTime' must be greater than the processing time for the safety-related application. If the 'CycleTime' parameter is smaller than or too close to the processing time, a cycle time violation may occur. The 'CycleTime' value must be an integer multiple of the Sercos cycle time. Proceed as follows to determine the correct SLC 'CycleTime' parameter value for your application:
|
During the commissioning phase described above, the SLC runs with the maximum cycle time. This results in a safety response time of the safety-related application which is possibly higher than required for your safety function.
WARNING
NON-CONFORMANCE TO SAFETY FUNCTION REQUIREMENTS
Verify the impact of the increased safety response time.
Make certain that appropriate procedures and measures (according to applicable sector standards) have been taken to help avoid hazardous situations during the commissioning phase.
Do not enter the zone of operation while running the SLC with the maximum cycle time.
Ensure that no other persons can access the zone of operation while running the SLC with the maximum cycle time.
Use appropriate safety interlocks where personnel and/or equipment hazards exist.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Parameter: SSDOCreation
|
Default value |
5 per cycle |
|
Unit |
-/- |
|
Description |
Defines the number of acyclic processing steps per Safety Logic Controller cycle. It can be used to optimize the boot behavior of the system. |
|
Possible values |
|
Parameter: NodeGuardingTimeout
|
Default value |
60 |
|
Value range Step size |
30...3,000 1 |
|
Unit |
s |
|
Description |
Sets the period (timeout value) to put the safety-related modules in pre-operational state when the Safety Logic Controller is incommunicative or in case of communication errors detected between the safety-related module and the Safety Logic Controller. It also defines the delay for the Safety Logic Controller to detect an unavailable module. To be observed:
|
Parameter: NumberOfScans:
|
Default value |
5 |
|
Value range Step size |
1...10 1 |
|
Unit |
-/- |
|
Description |
Specifies the number of module scans the Safety Logic Controller performs if it cannot correctly detect the configured safety-related modules before it indicates that one or more modules are unavailable (MXCHG flashing rapidly). Scanning is continued even after the SLC has triggered the LED for unavailable modules. |
Parameter: RemoteControlAllowed
|
Default value |
No |
|
Unit |
-/- |
|
Description |
Enables or disables the remote control of the Safety Logic Controller. NOTE: Remote controlling the Safety Logic Controller can be done using the function blocks provided in the 'SLCRemoteController' library in EcoStruxure Machine Expert. |
|
Parameter value |
|
The manufacturer or the operating company of the machine must take into consideration the inherent hazards involved in a remote control operation to avoid unintentional equipment operation.
WARNING
UNINTENDED EQUIPMENT OPERATION
Place operator devices of the control system near the machine or in a place where you have full view of the machine.
Protect operator commands against unauthorized access.
If remote control is a necessary design aspect of the application, ensure that there is a local, competent, and qualified observer present when operating from a remote location.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Group: SafetyResponseTimeDefaults
The safety response time is the time between the arrival of the sensor signal on the input channel of a safety-related input module and the shut-off signal at the output channel of a safety-related module. The parameters in this group influence the safety response time of the Safety Logic Controller system. For further and detailed background information, refer to the topic "Safety Response Time".
Beside this 'SafetyResponseTimeDefaults' group, each module has its own 'SafetyResponseTime' group. The parameters in the Safety Logic Controller 'SafetyResponseTimeDefaults' group are applied to the safety-related modules for which the ManualConfiguration parameter is set to 'No'. This way, the parameters relevant for the safety response time can be configured identically for the modules involved in the application. Each safety-related input or output module for which ManualConfiguration is set to 'Yes' uses the parameter values specifically set for itself.
Parameter: MinDataTransportTime
|
Default value |
12 |
|
Value range Step size |
12...500 1 |
|
Unit |
100 µs |
|
Description |
Defines the minimum time that is required to transmit a data telegram from a producer to a consumer. If a telegram is received earlier (by the consumer) than specified by this parameter value, communication is considered as invalid. EcoStruxure Machine Expert - Safety provides a calculator dialog to determine this parameter value. Term definition and background information According to the openSAFETY specification, devices (safety-related I/O modules as well as the Safety Logic Controller) communicate by sending and receiving cyclic data, referred to as openSAFETY telegrams. A telegram generating (sending) device is designated as producer, a receiving device is a consumer. Each telegram includes a time stamp for time validation of the communication. On receipt of a telegram, the consumer compares this time stamp with the present time. If the schedule is kept, the communication is considered as valid. If a telegram is received earlier than defined by this parameter, communication is considered as invalid and is not further processed. The 'SafeModuleOK' process data item also becomes SAFEFALSE indicating that the safety-related communication of the module is no longer valid. |
|
Value calculation |
How to calculate the MinDataTransportTime value
|
|
Practical values |
Entering the MinDataTransportTime value calculated in EcoStruxure Machine Expert - Safety results in a stable running system. |
Parameter: MaxDataTransportTime
|
Default value |
200 |
|
Value range Step size |
12...65,000 1 |
|
Unit |
100 µs |
|
Description |
Defines the maximum time that is allowed to transmit a data telegram from a producer to a consumer. If a telegram is received later (by the consumer) than specified by this parameter value, communication is considered as invalid. EcoStruxure Machine Expert - Safety provides a calculator dialog to determine this parameter value. NOTE: The parameter value influences the safety response time calculated by EcoStruxure Machine Expert - Safety. Term definition and background information According to the openSAFETY specification, devices (safety-related I/O modules as well as the Safety Logic Controller) communicate by sending and receiving cyclic data, referred to as openSAFETY telegrams. A telegram generating (sending) device is designated as producer, a receiving device is a consumer. Each telegram includes a time stamp for time validation of the communication. On receipt of a telegram, the consumer compares this time stamp with the present time. If the schedule is kept, the communication is considered as valid. If a telegram is delayed, communication is considered as invalid and is not further processed. The implications for the rest of the safety-related systems depend on the defined safety-related function. |
|
Value calculation |
How to calculate the MaxDataTransportTime value
|
|
Practical values |
Entering the MaxDataTransportTime value calculated in EcoStruxure Machine Expert - Safety results in a stable running system. |
Parameter: CommunicationWatchdog
|
Default value |
200 |
|
Value range Step size |
1...65,535 1 |
|
Unit |
100 µs |
|
Description |
Defines the maximum time period within which a consumer must receive a valid data telegram from a producer in order to consider the safety-related communication as valid and continue the application. The parameter sets a watchdog timer which then monitors whether a consumer receives telegrams from a producer in time. If the watchdog expires, communication is considered as invalid. EcoStruxure Machine Expert - Safety provides a calculator dialog to determine this parameter value. NOTE: The parameter value influences the safety response time calculated by EcoStruxure Machine Expert - Safety. Term definition and background information According to the openSAFETY specification, devices (safety-related I/O modules as well as the Safety Logic Controller) communicate by sending and receiving cyclic data, referred to as openSAFETY telegrams. A telegram generating (sending) device is designated as producer, a receiving device is a consumer. The CommunicationWatchdog value physically depends on the transport time needed for the telegram to be transmitted from a producer to a consumer and influences the worst case response time of the system. The calculated parameter value therefore depends on the MaxDataTransportTime parameter value. If the consumer receives the telegram in time (communication watchdog is not yet expired and the transmission time is within the period specified by the parameters MinDataTransportTime and MaxDataTransportTime), the watchdog timer is restarted and communication is considered as valid. The time stamp contained in the received telegram is not evaluated, only the receipt of a valid telegram is relevant. If no telegram is received (due to delay or loss) and the communication watchdog expires in the consumer, the module is set to the defined safe state. The 'SafeModuleOK' process data item also becomes SAFEFALSE indicating that the safety-related communication of the module is no longer valid. |
|
Value calculation |
How to calculate the CommunicationWatchdog value
|
|
Values |
For the CommunicationWatchdog value which you must enter in the parameter grid ('Devices' window), the following applies:
|
Group: Commissioning
Parameter: SafeMachineOptionxx
|
This parameter is only available for the SLC200 controller type. |
|
|
Default value |
OFF |
|
Unit |
-/- |
|
Description |
Allows to activate (enable) or deactivate (disable) a particular safety-related module (machine option) during start-up. This way, modular systems can be controlled partially or entirely. These are commissioning parameters, i.e., they can be set by users of the 'Commissioning' user group. Background information For each machine option, a process data item is available under the SLC\SafeMachineOptions node in the devices tree ('Devices' window). By dragging such an item into the FBD/LD code editor, they can be used in the application as SAFEBOOL variables. When connecting such a variable, for example, to the ACTIVATE input of a safety-related PLCopen function block, its value enables/disables the safety-related function covered by this safety-related function block. Setting the parameter value of a particular machine option to OFF/ON, directly sets/resets the assigned safety-related variable and can therefore be used to activate/deactivate, for example, all input and/or output on a safety-related module. |
|
Parameter value |
|
Process data items of the Safety Logic Controller
DataType xxx
|
Description |
SLC standard signals of various data types, transferred to or received from the standard (non-safety-related) controller. xxx is the signal ID. |
|
Data types |
Signals of various data types are provided: BOOL, INT, UINT, UDINT. |
|
Access type |
|
|
Possible values |
If the communication between the Safety Logic Controller and the standard (non-safety-related) controller is working correctly and SafeModuleOK = SAFETRUE, the possible values depend on the data type of the variable (only standard data types). |