The following description is valid for the function block SF_Antivalent_V1_0z, Version 1.0z (where z = 0 to 9).
Short description
|
The safety-related SF_Antivalent function block monitors the signals of two safety-related input terminals for different signal states. Typically, these signals come from two-channel sensors or switches such as an emergency-stop control device. The S_AntivalentOut enable signal becomes SAFETRUE when the S_ChannelNC and S_ChannelNO inputs switch as follows within the time set at DiscrepancyTime:
|
|
For this to happen, the function block must be activated (Activate = TRUE) and it must not have detected any errors (Error = FALSE).
NOTE:
Permanent signals (S_ChannelNC = SAFETRUE and S_ChannelNO = SAFEFALSE) at the inputs when the function block is activated (Activate = TRUE) or when the Safety Logic Controller is started up switch the enable signal (S_AntivalentOut) to SAFETRUE.
NOTE:
Always connect the two inputs differently, i.e., with a combination of one N/C contact signal and one N/O contact signal.
Function block inputs
Click the corresponding hyperlinks to obtain detailed information on the items below.
|
Name |
Short description |
Value |
|
State-controlled input for activating the function block. Data type: BOOL Initial value: FALSE |
|
|
|
State-controlled input for the NC channel of the connected two-channel switch or sensor. Data type: SAFEBOOL Initial value: SAFEFALSE |
|
|
|
State-controlled input for the NO channel of the connected two-channel switch or sensor. Data type: SAFEBOOL Initial value: SAFEFALSE |
|
|
|
Input for specifying the maximum permissible discrepancy time in seconds. Data type: TIME Initial value: #0ms If a change in state at an input results in both inputs having the same signals, the discrepancy time measurement starts. The second input must also then modify its state within the discrepancy time, so that both the S_ChannelNC and S_ChannelNO inputs have different signals again. If this does not happen, an error message will be output (Error = TRUE) and output S_AntivalentOut = SAFEFALSE. |
Enter a time value according to your risk analysis. Refer to the hazard message below this table. |
WARNING
NON-CONFORMANCE TO SAFETY FUNCTION REQUIREMENTS
Verify that the time value set at DiscrepancyTime corresponds to your risk analysis.
Be sure that your risk analysis includes an evaluation for incorrectly setting the time value for the DiscrepancyTime parameter.
Validate the overall safety-related function with regard to the set DiscrepancyTime value and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Function block outputs
|
Name |
Short description |
Value |
|
Output for signaling "Function block activated/not activated". Data type: BOOL |
|
|
|
Output for enable signal of the function block. Data type: SAFEBOOL Refer to the hazard message below this table. |
|
|
|
Output for error message. Data type: BOOL NOTE: To reset the error message, SAFEFALSE must be present at the S_ChannelNC input and SAFETRUE at input S_ChannelNO. |
|
|
|
Output for diagnostic message. Data type: WORD |
Diagnostic message of the function block. The possible values are listed and described in the topic "Diagnostic codes". |
The function block supports a safety-related monitoring function but not a safety-related control function.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the S_AntivalentOut enable signal does not directly control the safety process.
Validate the overall safety-related function, including the start-up behavior of the process, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
The example below shows a typical signal curve, such as may apply to the different signals S_ChannelNC = SAFETRUE and S_ChannelNO = SAFEFALSE within the discrepancy time.
NOTE:
The signal sequence diagrams in this documentation possibly omit particular diagnostic codes. For example, a diagnostic code is possibly not shown if the related function block state is a temporary transition state and only active for one cycle of the Safety Logic Controller.
Only typical input signal combinations are illustrated. Other signal combinations are possible.
|
0 |
The function block is not yet activated (Activate = FALSE). As a result, all outputs are FALSE or SAFEFALSE. |
|
1 |
Function block activation (Activate = TRUE). In the meantime, input S_ChannelNC = SAFEFALSE and S_ChannelNO = SAFETRUE. The S_AntivalentOut output remains SAFEFALSE. |
|
2 |
The S_ChannelNO input remains SAFETRUE and the S_ChannelNC input switches to SAFETRUE. When the state of an input switches, the discrepancy time measurement starts. |
|
3 |
S_AntivalentOut switches to SAFETRUE, as both inputs switch during the time set at DiscrepancyTime (S_ChannelNC from SAFEFALSE to SAFETRUE and S_ChannelNO from SAFETRUE to SAFEFALSE). This results in antivalent signals at the inputs. |
|
4 |
S_AntivalentOut switches to SAFEFALSE, as S_ChannelNO switches to SAFETRUE. The discrepancy time measurement starts when the state at S_ChannelNO changes. |
|
5 |
S_AntivalentOut and Error remain FALSE, as input S_ChannelNC switches to SAFEFALSE during the discrepancy time. |
|
6 |
S_ChannelNO switches to SAFEFALSE. This change in state causes the discrepancy time measurement to start again. |
|
7 |
S_AntivalentOut switches to SAFETRUE, as S_ChannelNC switches to SAFETRUE during the discrepancy time, resulting in antivalence again. |
|
8 |
S_AntivalentOut switches to SAFEFALSE, as the antivalence comes to an end (S_ChannelNC becomes SAFEFALSE). The discrepancy time measurement starts when the state at S_ChannelNC modifies. S_AntivalentOut and Error remain FALSE, as the second input also changes its state during the discrepancy time (S_ChannelNO becomes SAFETRUE). |
NOTE:
The other signal sequence diagram can also be taken into account.
This example illustrates two-channel control of the safety-related SF_EmergencyStop function block with the help of the SF_Antivalent function block.
The emergency-stop control device is connected to the inputs I0 and I1 of the safety-related input device SDI with an ID of 1. The N/C and N/O contacts of the emergency-stop control device are connected to the safety-related SF_Antivalent function block for evaluation purposes.
The S_AntivalentOut enable signal of the safety-related SF_Antivalent function block resulting from this is connected to the safety-related SF_EmergencyStop function block for further evaluation. The S_AntivalentOut output of the safety-related SF_Antivalent function block becomes SAFETRUE when the S_ChannelNC and S_ChannelNO inputs switch as follows within the time set at DiscrepancyTime:
S_ChannelNC from SAFEFALSE to SAFETRUE
and S_ChannelNO from SAFETRUE to SAFEFALSE.
A start-up inhibit (after the Safety Logic Controller has been started up or after the function block has been activated) as well as a restart inhibit (after the emergency-stop control device has been deactivated) is set for the safety-related SF_EmergencyStop function block. Both inhibits are removed by pressing the reset button connected to input NI0 of the standard input device DI with an ID of 1.
NOTE:
The enable output S_EStopOut of the SF_EmergencyStop function block is directly connected to a global I/O variable or to an output terminal of the application via additional safety-related functions/function blocks.
Connect the S_EStopOut enable output of the SF_EmergencyStop function block to the S_OutControl input of the SF_EDM function block, for example, thus implementing a two-channel output connection.
Further Information
For more detailed information, refer to the description of the corresponding safety-related function block.
|
S1 |
Emergency-stop |
|
S2 |
Reset |
|
|
See note above the illustration |
Further Information
The second application example and the accompanying notes can also be taken into account.
Detailed information
Additional information is available in the following sections: