Additional application examples

Further Information

Refer also to the application example found in the overview for this function block.

This section contains additional possible two-channel applications, in which the function block is used to monitor two contactors.

The safety-related function block must only be used in an actual applica­tion once a risk analysis has been conducted.

Details of the risk category/SIL/PL have not been included here, as clas­sification is always based on the application in which the function block is used.

NOTE:

The use of the safety-related function block alone is not sufficient to execute the safety-related function according to the Cat./SIL/PL determined by the risk analysis. In conjunction with the safety-related I/O device used, additional measures must be taken to meet the requirements of the safety-related function. These include, for example, the appropriate wiring and parameterization of the inputs and outputs as well as measures to exclude (design out) errors that cannot be detected. For additional information, refer to the documentation provided with the safety-related I/O device used.

NOTE:

Refer to the notes in the User Manual on proper electrical connec­tion of the Safety Logic Controller and the extension modules (e.g., connecting the contactors).

Separate feedback from two contactors (two-channel application up to Cat. 4)

In this example, the safety-related SF_EDM function block controls the two contactors Q1 and Q2 connected to outputs O0 and O1 of the Safety Logic Controller.

Separate feedback is provided from each contactor via an N/C contact to the input terminals I0 and I1 of the safety-related input device SDI 1. The feedback signal of contactor Q1 at terminal I0 is assigned to the global I/O variable Q1_Feedback, which in turn is connected to the S_EDM1 function block input. The signal of contactor Q2 at terminal I1 is connected to the S_EDM2 function block input via the Q2_Feedback variable.

The reset button S1 is connected to the input terminal NI0 of the stan­dard input device DI 1. The global I/O variable S1_Reset_EDM assigned to the signal is connected to the Reset input. The signal is used to remove the start-up inhibit and reset the error states after the cause of the error has been removed.

NOTE:

The S_OutControl input is controlled by another safety-related function block or a safety-related function within the program.

PROG_EDM_ApplicationExample2.png

Q1, Q2

Load contactor with positively driven contacts.

S1

Reset

noteOnImage.png 

See note above the illustration.

Combined feedback from two contactors (two contactor contacts in series) (two-channel application up to Cat. 4)

In this example, the safety-related SF_EDM function block controls the two contactors Q1 and Q2 connected to outputs O0 and O1 of the Safety Logic Controller.

Feedback is provided from each contactor via an N/C contact. The N/C contacts are connected in series and routed to input terminal I0 of the safety-related input device SDI 1. The signal of terminal I0 is assigned to the global I/O variable Q1Q2_Feedback, which in turn is connected to both function block inputs S_EDM1 and S_EDM2.

The reset button S1 is connected to the input terminal NI0 of the stan­dard input device DI 1. The global I/O variable S1_Reset_EDM assigned to the signal is connected to the Reset input. The button signal is used to remove the start-up inhibit and reset the error states after the cause of the error has been removed.

NOTE:

The S_OutControl input is controlled by another safety-related function block or a safety-related function within the program.

PROG_EDM_ApplicationExample3.png

Q1, Q2

Load contactor with positively driven contacts.

S1

Reset

noteOnImage.png 

See note above the illustration.