Implementation of safety requirements from applicable standards

The safety-related function block has been developed according to the safety requirements (from applicable standards) listed in this section. All other requirements from these standards must be observed when imple­menting the safety-related function.

This section describes either how the function block meets the require­ments of the standards or what measures need to be taken to meet the requirements of the standards.

Standards

Context/Requirement

Implementation

EN ISO 12100-2

Start-up after failure of supply voltage/spontaneous restart

The function block supports a start-up inhibit and/or restart inhibit of the function block after

  • start-up of the Safety Logic Controller or activation of the func­tion block (S_StartReset = SAFEFALSE)

  • deactivating of the emergency-stop control device (S_AutoReset = SAFEFALSE)

You are responsible for planning and implementing the start-up/restart behavior according to your risk analysis. To prevent an unintended start-up/restart, you may need to perform an additional function start once the safety-related function has been reset. This will depend on both the results of the risk analysis and the signal path of the reset signal.

EN ISO 13849-1

Manual reset device

The Reset input supports the function of a manual reset device.

NOTE:

Resetting does not occur with a negative (falling) edge, as specified by standard ISO 13849-1, but with a positive (rising) edge.

EN ISO 13849-1

Category B to 4

Single-channel or two-channel connection must be established depending on the category.

NOTE:

Cross-circuit monitoring  is not performed by the function block. It is your responsi­bility to implement this monitoring function outside of this function block in the safety-related control system. For example, an Equivalent function block must be connected upstream for the purpose of evaluating signals if a two-channel emer­gency-stop control device with two N/C contacts is used.

ISO 13850

Positive opening operation

Only use approved emergency-stop control devices which conform to standard ISO 13850.

ISO 13850

Priority of emergency-stop

When connecting the emergency-stop signals, you must ensure that the emergency-stop command has priority over all other commands and is processed in every Safety Logic Controller cycle.

ISO 13850

Restarting

You can select whether the function block will support automatic restart or a restart inhibit after the emergency-stop control device has been deactivated.

ISO 13850

Emergency-stop function

When the manual control has been activated, the emergency-stop device must operate in a way that ensures danger is automatically negated or reduced as effectively as possible.

NOTE:

It is your responsibility to imple­ment this function outside of this function block in the control system.

ISO 13850/EN 60204

Requirements of electrical emergency-stop equipment

The emergency-stop equipment you use must meet the requirements of the relevant standards.

ISO 13850

Requirements of emergency-stop devices

It is your responsibility to meet the requirements of this standard, according to the risk analysis you carried out.

ISO 13850

Using wires and cables as manual controls

It is your responsibility to meet the requirements of this standard, according to the risk analysis you carried out.

EN 60204

Stop functions

The function block (S_EStopOut enable signal) executes stop category 0.