SF_EmergencyStop

 

The following description is valid for the function block SF_Emergen­cyStop_V1_0z, Version 1.0z (where z = 0 to 9).

Short description

The safety-related SF_Emergen­cyStop function block monitors the switching states of an emer­gency-stop control device. When the connected emergency-stop device is activated, the enable signal at output S_EStopOut becomes SAFEFALSE.

S_StartReset can be used to specify a start-up inhibit and S_AutoReset can be used to specify a restart inhibit.

PROG_EmergencyStop_ico_editor.png

Function block inputs

Click the corresponding hyperlinks to obtain detailed information on the items below.

Name

Short description

Value

Activate

State-controlled  input for activating the function block.

Data type: BOOL

Initial value: FALSE

  • FALSE: Function block inactive

  • TRUE: Function block activated

S_EStopIn

State-controlled  input for the status of the emergency-stop control device.

Data type: SAFEBOOL

Initial value: SAFEFALSE

  • SAFEFALSE: Emer­gency-stop control device is activated

  • SAFETRUE: Emer­gency-stop control device is not acti­vated

S_StartReset

State-controlled  input for specifying the start-up inhibit after the Safety Logic Controller has been started up or the function block has been activated.

An active start-up inhibit must be removed manually by means of a positive signal edge at the Reset input. A deactivated start-up inhibit causes the S_EStopOut output to switch to SAFETRUE automatically when the function block is activated and the safety-related function is not requested.

Data type: SAFEBOOL

Initial value: SAFEFALSE

Refer to the first hazard message below this table.

  • SAFEFALSE: With start-up inhibit

  • SAFETRUE: Without start-up inhibit

S_AutoReset

State-controlled  input for specifying the restart inhibit after the SAFETRUE signal has returned at the S_EStopIn input, i.e., after the previously activated emergency-stop control device has been deactivated again.

An active restart inhibit must be removed manually by means of a positive signal edge at the Reset input. A deactivated restart inhibit causes the S_EStopOut output to switch to SAFETRUE automatically when the function block is activated and the safety-related function is no longer requested.

Data type: SAFEBOOL

Initial value: SAFEFALSE

Refer to the first hazard message below this table.

  • SAFEFALSE: With restart inhibit

  • SAFETRUE: Without restart inhibit

Reset

Edge-triggered  input for the reset signal:

  • Resetting error messages when the cause of the error is no longer present.

  • Manual resetting of an active start-up/restart inhibit (specified by S_Star­tReset and/or S_Au­toReset).

Refer to the second hazard message below this table.

Data type: BOOL

Initial value: FALSE

NOTE:

Resetting does not occur with a negative (falling) edge, as specified by standard EN ISO 13849-1, but with a posi­tive (rising) edge.

  • FALSE: Reset is not requested

  • Edge FALSE > TRUE: Reset is requested

WARNING

NON-CONFORMANCE TO SAFETY FUNCTION REQUIRE­MENTS

  • Verify the impact of a deactivated start-up inhibit (S_StartReset = SAFETRUE) and/or restart inhibit (S_AutoReset = SAFETRUE) on your machine or process prior to implementation.

  • Observe the regulations given by relevant sector standards regarding the start-up/restart inhibit.

  • Verify that a suitable start-up inhibit is in place at another location or using other means.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Resetting the function block by means of a positive signal edge at the Reset input can cause the S_EStopOut output to switch to SAFETRUE immediately (depending on the status of the other inputs).

WARNING

UNINTENDED START-UP

  • Include in your risk analysis the impact of the reset by means of a positive signal edge at the Reset input.

  • Make certain that appropriate procedures and measures (according to applicable sector standards) have been established to help avoid hazardous situations when resetting.

  • Do not enter the zone of operation when resetting.

  • Ensure that no other persons can access the zone of operation when resetting.

  • Use appropriate safety interlocks where personnel and/or equip­ment hazards exist.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Function block outputs

Click the corresponding hyperlinks to obtain detailed information on the items below.

Name

Short description

Value

Ready

Output for signaling "Function block activated/not activated".

Data type: BOOL

  • TRUE: Function block is activated (Activate = TRUE) and the output parameters repre­sent the state of the safety-related func­tion.

  • FALSE: Function block is not activated (Activate = FALSE) and all outputs of the function block are switched to FALSE/SAFE­FALSE.

S_EStopOut

Output for enable signal of the function block.

Data type: SAFEBOOL

  • SAFEFALSE:

    • Emergency-stop control device is acti­vated

    • or the function block is not activated

    • or the start-up/restart inhibit is active

    • or the error message is present.

  • SAFETRUE:

    • Emergency-stop control device is not activated

    • and the function block is activated

    • and the start-up/restart inhibit is not active

    • and no error message is present.

Error

Output for error message.

Data type: BOOL

  • FALSE: No error is present.

  • TRUE: The function block has detected an error. The S_EStopOut output switches to SAFE­FALSE as a result.

DiagCode

Output for diagnostic message.

Data type: WORD

Diagnostic message of the function block.

The possible values are listed and described in the topic "Diagnostic codes".

Signal sequence diagram

This diagram relates to a typical emergency-stop function with an active start-up inhibit and an active restart inhibit:

NOTE:

The other signal sequence diagram can be taken into account.

NOTE:

The signal sequence diagrams in this documentation possibly omit particular diagnostic codes. For example, a diagnostic code is possibly not shown if the related function block state is a temporary transition state and only active for one cycle of the Safety Logic Controller.

Only typical input signal combinations are illustrated. Other signal combinations are possible.

PROG_EmergencyStop_Signal1.png

0

The function block is not yet activated (Activate = FALSE).

As a result, all outputs are FALSE or SAFEFALSE.

1

After the function block has been activated by Activate = TRUE, the start-up inhibit is active at first.

2

The previously activated emergency-stop control device is deactivated (N/C contacts closed). The S_EStopOut output remains SAFEFALSE at first, as S_StartReset = SAFEFALSE prevents automatic start-up.

3

Positive signal edge at the Reset input removes the start-up inhibit, followed by normal operation. The S_EStopOut output becomes SAFETRUE.

4

Emergency-stop request. The control device is activated. The S_EStopOut output becomes SAFEFALSE.

5

The emergency-stop control device is deactivated again and the S_EStopOut output remains SAFEFALSE at first, as the restart inhibit has been specified by S_AutoReset = SAFEFALSE.

6

Positive signal edge at the Reset input removes the start-up inhibit, followed by normal operation. The S_EStopOut output becomes SAFETRUE.

7

The function block activation is reset (Activate = FALSE), S_EStopOut output = SAFEFALSE.

Application example

This example illustrates a single-channel connection of the N/C contact of an emergency-stop control device S1 with the safety-related SF_EmergencyStop function block. The emergency-stop control device is connected to input terminal I0 of the safety-related input device SDI with an ID of 1.

In this example the following applies:

The function block is perpetually activated by the TRUE constant at the Activate input.

S_StartReset = SAFEFALSE specifies a start-up inhibit after the Safety Logic Controller has been started up or the function block has been acti­vated. Furthermore, S_AutoReset = SAFEFALSE specifies a restart inhibit of the function block after the emergency-stop control device has been deactivated, i.e., once the SAFETRUE signal has returned at the S_EStopIn input. Both inhibits are only removed when there is a positive signal edge at the Reset input.

To this end, the S2 reset button is connected to input NI0 of the standard input device DI 1.

PROG_EmergencyStop_ApplicationExample1.png

S1

Emergency-stop

S2

Reset

Further Information

The other application examples and the accompanying notes can be taken into account.

Detailed information

Additional information is available in the following sections: