DiscrepancyTime input

Specification of the permissible discrepancy time for monitoring the switching operation at the S_ChannelA and S_ChannelB inputs.

Data type: TIME

Initial value: #0ms

Connection: Connect this input to a time literal, i.e., to a constant of the data type TIME.

Background: As a result of mechanical influences, signals may have a tolerance when switching contacts. By specifying the DiscrepancyTime value, the time period is defined within which the switching operations at the inputs S_ChannelA and S_ChannelB must occur to be recognized as simultaneous. This means both inputs can switch to SAFETRUE or SAFEFALSE within the set discrepancy time.

NOTE:

The switchover from SAFEFALSE to SAFETRUE is monitored for both inputs, as well as the switchover from SAFETRUE to SAFEFALSE.

WARNING

NON-CONFORMANCE TO SAFETY FUNCTION REQUIRE­MENTS

  • Verify that the time value set at DiscrepancyTime corresponds to your risk analysis.

  • Be sure that your risk analysis includes an evaluation for incorrectly setting the time value at the DiscrepancyTime parameter.

  • Validate the overall safety-related function with regard to the set DiscrepancyTime value and thoroughly test the application.

Failure to follow these instructions can result in death, serious injury, or equipment damage.