SF_GuardMonitoring

 

The following description is valid for the function block SF_GuardMoni­toring_V1_0z, Version 1.0z (where z = 0 to 9).

Short description

The safety-related SF_GuardMonitoring function block monitors a guard (e.g., door) with two-stage interlocking according to the EN 1088 standard.

S_StartReset can be used to specify a start-up inhibit and S_AutoReset can be used to specify a restart inhibit.

PROG_GuardMonitoring_icon_editor.png

Function block inputs

Click the corresponding hyperlinks to obtain detailed information on the items below.

Name

Short description

Value

Activate

State-controlled  input for activating the function block.

Data type: BOOL

Initial value: FALSE

  • FALSE: Function block inactive

  • TRUE: Function block activated

S_GuardSwitch1  and S_GuardSwitch2

State-controlled  inputs for the connected position switches of the door.

For the S_GuardMonitoring output to switch to SAFETRUE, both inputs S_GuardSwitch1 and S_GuardSwitch2 must switch to SAFETRUE within the time set at DiscrepancyTime.

Data type: SAFEBOOL

Initial value: SAFEFALSE

NOTE:

If only one signal reports the status of the door (one position switch only), this must be connected in parallel to both inputs S_Guard­Switch1 and S_Guard­Switch2. Where this is the case, a time of 0 seconds must be set at Discrep­ancyTime.

  • SAFEFALSE: Posi­tion switch reports open state

  • SAFETRUE: Posi­tion switch reports closed state

DiscrepancyTime

Input for specifying the maximum permissible discrepancy time for the closing operation of the safety equipment.

Data type: TIME

Initial value: #0ms

If S_GuardSwitch1 or S_GuardSwitch2 switches to SAFETRUE, the respective other input (S_GuardSwitch1 or S_GuardSwitch2) must also switch to SAFETRUE within the time set at DiscrepancyTime for the switching operation to be considered as valid.

If not both inputs have switched to SAFETRUE after the time set at DiscrepancyTime has elapsed, an error message is generated (Error = TRUE) and the S_GuardMonitoring output remains in the defined safe state SAFE­FALSE.

Enter a time value according to your risk analysis.

Refer to the first hazard message below this table.

S_StartReset

State-controlled  input for specifying the start-up inhibit after the Safety Logic Controller has been started up or the function block has been activated.

Data type: SAFEBOOL

Initial value: SAFEFALSE

An active start-up inhibit must be removed manually by a positive signal edge at the Reset input. A deactivated start-up inhibit causes the S_GuardMonitoring output to switch to SAFETRUE automatically when the function block is activated and the safety-related function is not requested.

Refer to the second hazard message below this table.

  • SAFEFALSE: With start-up inhibit

  • SAFETRUE: Without start-up inhibit

S_AutoReset

State-controlled  input for specifying the restart inhibit after the previously opened safety equipment has been closed (in other words, after the SAFETRUE signal has returned at inputs S_GuardSwitch1 and S_GuardSwitch2).

Data type: SAFEBOOL

Initial value: SAFEFALSE

An active restart inhibit must be removed manually by a positive signal edge at the Reset input. A deactivated restart inhibit causes the S_GuardMonitoring output to switch to SAFETRUE automatically when the function block is activated and the safety-related function is no longer requested.

Refer to the second hazard message below this table.

  • SAFEFALSE: With restart inhibit

  • SAFETRUE: Without restart inhibit

Reset

Edge-triggered  input for the reset signal:

  • Resetting error messages when the cause of the error is no longer present.

  • Manual resetting of an active start-up/restart inhibit (specified by S_Star­tReset and/or S_Au­toReset).

Refer to the third hazard message below this table.

Data type: BOOL

Initial value: FALSE

NOTE:

Resetting does not occur with a negative (falling) edge, as specified by standard EN ISO 13849-1, but with a posi­tive (rising) edge.

  • FALSE: Reset is not requested

  • Edge FALSE > TRUE: Reset is requested

WARNING

NON-CONFORMANCE TO SAFETY FUNCTION REQUIRE­MENTS

  • Verify that the time value set at DiscrepancyTime corresponds to your risk analysis.

  • Be sure that your risk analysis includes an evaluation for incorrectly setting the time value at the DiscrepancyTime parameter.

  • Validate the overall safety-related function with regard to the set DiscrepancyTime value and thoroughly test the application.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

WARNING

NON-CONFORMANCE TO SAFETY FUNCTION REQUIRE­MENTS

  • Verify the impact of a deactivated start-up inhibit (S_StartReset = SAFETRUE) and/or restart inhibit (S_AutoReset = SAFETRUE) on your machine or process prior to implementation.

  • Observe the regulations given by relevant sector standards regarding the start-up/restart inhibit.

  • Verify that a suitable start-up inhibit is in place at another location or using other means.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Resetting the function block by means of a positive signal edge at the Reset input can cause the S_GuardMonitoring output to switch to SAFETRUE immediately (depending on the status of the other inputs).

WARNING

UNINTENDED START-UP

  • Include in your risk analysis the impact of the reset by means of a positive signal edge at the Reset input.

  • Make certain that appropriate procedures and measures (according to applicable sector standards) have been established to help avoid hazardous situations when resetting.

  • Do not enter the zone of operation when resetting.

  • Ensure that no other persons can access the zone of operation when resetting.

  • Use appropriate safety interlocks where personnel and/or equip­ment hazards exist.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

Function block outputs

Name

Short description

Value

Ready

Output for signaling "Function block activated/not activated".

Data type: BOOL

  • FALSE: Function block is not activated (Activate = FALSE) and all outputs of the function block are switched to FALSE/SAFE­FALSE.

  • TRUE: Function block is activated (Activate = TRUE) and the output parameters repre­sent the state of the safety-related func­tion.

S_GuardMonitoring

Output for enable signal of the function block.

Data type: SAFEBOOL

  • SAFEFALSE:

    • The guard is not closed (S_Guard­Switch1 and/or S_GuardSwitch2 = SAFEFALSE)

    • or the function block is not activated

    • or the start-up/restart inhibit is active

    • or an error message is present.

  • SAFETRUE:

    • Guard closed (S_GuardSwitch1 and S_Guard­Switch2 = SAFETRUE)

    • and the function block is activated

    • and the start-up/restart inhibit is not active

    • and no error message is present.

Error

Output for error message.

Data type: BOOL

  • FALSE: No error is present.

  • TRUE: The function block has detected an error. The S_GuardMonitoring output switches to SAFEFALSE as a result.

DiagCode

Output for diagnostic message.

Data type: WORD

Diagnostic message of the function block.

The possible values are listed and described in the topic "Diagnostic codes".

Signal sequence diagram

This diagram is based on typical monitoring of a guard with two-stage interlocking, where both position switches connected to inputs S_Guard­Switch1 and S_GuardSwitch2 switch within the time set at Discrepancy­Time.

Additional assumptions:

S_StartReset = SAFEFALSE: Start-up inhibit after the function block has been activated and the Safety Logic Controller has started up

S_AutoReset = SAFEFALSE: Restart inhibit after the previously opened safety equipment has been closed (i.e., after the SAFETRUE signals have returned at inputs S_GuardSwitch1 and S_GuardSwitch2).

NOTE:

The other signal sequence diagram can be taken into account.

NOTE:

The signal sequence diagrams in this documentation possibly omit particular diagnostic codes. For example, a diagnostic code is possibly not shown if the related function block state is a temporary transition state and only active for one cycle of the Safety Logic Controller.

Only typical input signal combinations are illustrated. Other signal combinations are possible.

PROG_GuardMonitoring_Signal1.png

0

The function block is not yet activated (Activate = FALSE).

As a result, all outputs are FALSE or SAFEFALSE.

1

Both inputs S_GuardSwitch1 and S_GuardSwitch2 are SAFETRUE. However, the S_GuardMonitoring output is still SAFEFALSE, since a start-up inhibit is specified after the Safety Logic Controller has been started up by S_StartReset = SAFEFALSE.

2

A positive edge at the Reset input resets the start-up inhibit and the S_GuardMonitoring output switches to SAFETRUE.

3

The safety equipment is opened. S_GuardSwitch2 and S_GuardSwitch1 switch to SAFEFALSE one after the other, and the S_GuardMonitoring output becomes SAFEFALSE.

4

The safety equipment is closed. Measurement of the discrepancy time begins with the switch from SAFEFALSE to SAFETRUE at S_GuardSwitch2. The second input S_GuardSwitch1 also switches to SAFETRUE during the time set at DiscrepancyTime.

As a restart inhibit is specified by S_AutoReset = SAFEFALSE after the safety equipment has been closed (S_GuardSwitch1 and S_GuardSwitch2 = SAFETRUE), the S_GuardMonitoring output only becomes SAFETRUE once the restart inhibit has been removed by a positive edge at the Reset input.

5

The safety equipment is opened. S_GuardSwitch1 and S_GuardSwitch2 switch to SAFEFALSE one after the other, and the S_GuardMonitoring output becomes SAFEFALSE.

6

The safety equipment is closed. Both inputs S_GuardSwitch1 and S_GuardSwitch2 become SAFETRUE at the same time. The function block detects the permanent TRUE signal at the Reset input as an error. Output Error becomes TRUE and output S_GuardMonitoring remains SAFEFALSE.

7

The Reset input becomes FALSE; this causes the error message to be reset.

Application example: Door monitoring using a mechanical position switch, start-up inhibits activated

This example describes how a mechanically activated position switch with 2 N/C contacts is evaluated using the safety-related SF_GuardMon­itoring function block. Position switch B1 is connected to input terminals I0 and I1 of safety-related input device SDI 1.

The signals from position switch B1 are evaluated, based on two chan­nels, for equivalence in the safety-related input device, which has been parameterized accordingly. The resulting signal is assigned to the global I/O variable B1_GMControl_In. This variable is connected to the inputs S_GuardSwitch1 and S_GuardSwitch2 of the safety-related SF_Guard­Monitoring function block for evaluation.

B1_GMControl_In is SAFETRUE if both inputs of the safety-related input device SDI 1 are SAFETRUE at the same time (safety equipment closed) and the safety-related input device SDI 1 does not report any errors as regards exceeding the time set at DiscrepancyTime.

NOTE:

Since only one signal reports the status of the door in this example (one position switch), this is connected in parallel to both inputs S_GuardSwitch1 and S_GuardSwitch2. In this case, a value of 0 seconds is set at input Discrepancy­Time.

The function block is perpetually activated by a TRUE constant at the Activate input.

S_StartReset = SAFEFALSE specifies a start-up inhibit after the Safety Logic Controller has been started up or the function block has been acti­vated. Furthermore, S_AutoReset = SAFEFALSE specifies a restart inhibit for the function block after the door has been closed. Both inhibits are only removed when there is a positive signal edge at the Reset input.

To this end, the S1 reset button is connected to input terminal NI0 of the standard input device DI 1. The terminal is assigned to the global I/O variable S1_Reset_GM, which in turn is connected to the function block input Reset.

NOTE:

The enable signal at the S_GuardMonitoring output of the SF_GuardMonitoring function block is connected to addi­tional safety-related function blocks or functions and controls the application accordingly.

PROG_GuardMonitoring_ApplicationExample1.png

S1

Reset

B1

Door switch with two positively driven N/C contacts for positive opening operation Symbol_Zwangsoeffnend.gif (SAFETRUE, if safety equipment closed).

(*1)

Door: open

(*2)

Door: closed

noteOnImage.png 

See note above the illustration.

Further Information

The other application examples and the accompanying notes can be taken into account.

Detailed information

Additional information is available in the following sections: