Functional description

The safety-related SF_MutingSeq function block executes the function "sequential muting with four sensors" within an application.

To this end, it evaluates the following signals:

A start-up inhibit can be specified at S_StartReset.

The function block switches the enable signal at the S_AOPD_Out output in accordance with the input signals present. It executes stop category 0 at this output.

NOTE:

The signal at the S_AOPD_Out output is the enable signal for the entire process. In order to process the enable or, equally, the request for the defined safe state in the functional safety system, the signal must be used in the safety logic in such a way that a SAFEFALSE signal at the S_AOP­D_Out output stops the zone of operation from being used.

NOTE:

Depending on the result of the risk analysis, optical, mechanical or inductive sensors such as reflection light sensors, mechanical or inductive switches can be used as muting sensors. Optical sensors serve as examples in the help information.

Muting operation

The overall muting operation is divided into different muting sequences.

NOTE:

Only the material flow direction from muting sensors Muting­Switch11PfeilTransRichtung.gifMutingSwitch12 to muting sensors MutingSwitch21PfeilTransRichtung.gifMut­ingSwitch22 is described in the following. This is illustrated in the graphic in the function block overview.

The function block also supports the opposite material flow direction from muting sensors MutingSwitch22PfeilTransRichtung.gifMutingSwitch21 to muting sensors MutingSwitch12PfeilTransRichtung.gifMutingSwitch11. The functional sequence remains identical.

  1. Protecting the zone of operation.

    The safety-related equipment is active when muting is not active: If the function block does not detect an active muting operation at the muting inputs, a SAFEFALSE signal from the light grid ("object detected") leads to the defined safe state SAFEFALSE at the S_AOPD_Out output (e.g., "stop machine").

  2. Activating the muting operation.

    The safety-related equipment is deactivated: When the muting sensors located before the safety-related equipment switch from FALSE to TRUE one after the other (i.e., first MutingSwitch11 and then MutingSwitch12) (because both have detected an object), the muting operation is activated and the safety-related equipment deactivated.

  3. Muting operation is active.

    The safety-related equipment is deactivated for as long as the muting operation is active and the sensors detect an object permissible for the muting operation.

    A SAFEFALSE signal from the light grid ("object detected") does in this case not cause the S_AOPD_Out output to switch to the defined safe state SAFEFALSE (e.g., "stop machine").

    The muting operation remains active as long as the requirements for a valid muting sequence are met and when the muting operation is completed properly within the maximum muting time set at MaxMuting­Time. If it is not, the S_AOPD_Out output switches to the defined safe state SAFEFALSE (e.g., "stop machine").

  4. Completing the muting operation.

    The safety-related equipment is active again. The muting operation is complete when the first muting sensor located behind the safety-related equipment (at the MutingSwitch21 input) switches back from TRUE to FALSE, i.e., an object is no longer detected in the detection area. The safety-related equipment is reactivated at the same time when the S_MutingActive output switches to SAFE­FALSE.

Further Information

Refer also to the "Invalid muting sequences" section in this context.

Example of a muting operation

The graphic below shows an example of a muting operation.

NOTE:

In the graphic, only the values of the inputs and outputs which are relevant for this illustration are given.

Explanatory notes:

PROG_MutingSeq_MutingProcess1.png 

The light beams of all the muting sensors are not interrupted. The muting operation is not (yet) active.

 PROG_MutingSeq_MutingProcess2.png 

  • The light beam of the first muting sensor (1) before the safety-related equipment is interrupted by an object on the transport conveyor.

  • This initiates the muting operation but muting is not active yet (S_MutingActive remains SAFEFALSE).

  • The MaxMutingTime timer starts (measures the dura­tion of the muting operation).

 PROG_MutingSeq_MutingProcess3.png 

  • The light beam of the first muting sensor remains inter­rupted.

  • The light beam of the second muting sensor is also interrupted.

    The requirements for a valid muting sequence are met because sensor 2 detected the object after sensor 1.

  • This starts the muting operation , i.e. muting is activated (S_MutingActive switches to SAFETRUE).

  • In this state the safety-related equipment is not active, i.e., SAFEFALSE at S_AOPD_In does not lead to SAFEFALSE at S_AOPD_Out.

 PROG_MutingSeq_MutingProcess4.png 

  • An object interrupts the light beam of the safety-related equipment, i.e., S_AOPD_In switches to SAFEFALSE. S_AOPD_Out remains SAFETRUE because the muting operation is still active.

  • The light beam of the first muting sensor after the safety-related equipment (3) is interrupted.

  • The requirements for a valid muting sequence are met because sensor 3 detected the object after sensors 1 and 2, and because the light beams of muting sensors 1 and 2 are still interrupted.

  • The MaxMutingTime timer continues to run.

 PROG_MutingSeq_MutingProcess5.png

  • The light beam of the fourth muting sensor is also inter­rupted.

    The requirements for a valid muting sequence are met because sensor 4 detected the object after sensors 1, 2 and 3, and because the light beams of muting sensors 1, 2 and 3 are still interrupted.

NOTE:

The muting sensors 1 and 2 must not report FALSE, before both sensors 3 and 4 have reported TRUE. Otherwise the function block detects an error.

  • As muting is still active, the S_AOPD_Out output remains SAFETRUE even though the light beam of the safety-related equipment is still interrupted.

 PROG_MutingSeq_MutingProcess6.png

  • The object is already behind the safety-related equip­ment, i.e., a SAFETRUE signal is present at the S_AOPD_In input again and the muting sensors 1 and 2 report FALSE again.

  • The light beam of muting sensor 3 is also not inter­rupted any more (sensor reports FALSE).

  • The change from TRUE to FALSE at input Muting­Switch21 stops the MaxMu­tingTime time measurement. As the muting operation has been completed within the time interval specified at MaxMu­tingTime, the S_AOPD_Out output remains SAFETRUE and no error is detected (Error remains FALSE).

  • Muting is inactive again.

  • In this state the safety-related equipment is active again, i.e., SAFE­FALSE at S_AOPD_In leads to SAFEFALSE at S_AOP­D_Out.

Invalid muting sequences

Invalid states at the muting sensors are detected as errors (Error = TRUE). In the event of an error, the S_AOPD_Out output always switches to the defined safe state (S_AOPD_Out = SAFEFALSE).

Invalid states always occur when the following valid muting operation is not adhered to:

Start-up inhibit (S_StartReset)

S_StartReset is used to specify the start-up inhibit after activating the function block and/or starting the Safety Logic Controller.

S_StartReset = SAFEFALSE

After the Safety Logic Controller has been started up and/or the function block has been activated at input Activate, the start-up inhibit is active. The start-up inhibit is only removed if there is a positive signal edge at the Reset input.

Refer to the first hazard message below this table.

S_StartReset = SAFETRUE

After the Safety Logic Controller has been started up and/or the function block has been activated at input Activate, no start-up inhibit is active.

Refer to the second hazard message below this table.

Removing the start-up inhibit by means of a positive signal edge at the Reset input can cause the S_AOPD_Out output to switch to SAFETRUE immediately (depending on the status of the other inputs).

WARNING

UNINTENDED START-UP

  • Verify the impact of removing the start-up inhibit by means of a positive signal edge at the Reset input.

  • Make certain that appropriate procedures and measures (according to applicable sector standards) have been taken to help avoid hazardous situations when removing the start-up inhibit.

  • Do not enter the zone of operation when removing the start-up inhibit.

  • Ensure that no other persons can access the zone of operation when removing the start-up inhibit.

  • Use appropriate safety interlocks where personnel and/or equip­ment hazards exist.

Failure to follow these instructions can result in death, serious injury, or equipment damage.

WARNING

NON-CONFORMANCE TO SAFETY FUNCTION REQUIRE­MENTS

  • Verify the impact of a deactivated start-up inhibit (S_StartReset = SAFETRUE) on your machine or process prior to implementation.

  • Observe the regulations given by relevant sector standards regarding the start-up inhibit.

  • Verify that a suitable start-up inhibit is in place at another location or using other means if the start-up inhibit is deactivated by setting S_StartReset = SAFETRUE.

Failure to follow these instructions can result in death, serious injury, or equipment damage.