The following description is valid for the function block SF_MutingSeq_V1_0z, Version 1.0z (where z = 0 to 9).
|
The safety-related SF_MutingSeq function block evaluates the signals of four muting sensors and an optoelectronic safety-related equipment (a light grid, for example) in an application for sequential muting with four sensors and switches the enable signal at the S_AOPD_Out output. The signal at the S_AOPD_Out output is the enable signal for the entire process. A SAFEFALSE signal at the S_AOPD_Out output stops the application in the zone of operation. This function can be used to temporarily deactivate (or "mute") safety-related equipment in the form of a light grid, for example, in order to allow an object which has been identified by the muting sensors as permissible (for the muting operation) to pass through on an assembly conveyor. In such a case, the interruption of the light grid does not have any effect on the S_AOPD_Out output. By contrast, if the safety-related equipment is engaged by an object which has not been identified by the muting sensors as permissible, the S_AOPD_Out output switches to SAFEFALSE. For example, if the hand of a worker passes through an assembly conveyer interrupting a light grid, the S_AOPD_Out output would be used to signal the actions necessary to set the zone of operation to its defined safe state. The maximum allowable time for the muting operation is monitored using the four muting sensors. Refer to the following representation to view the arrangement of the muting sensors. A start-up inhibit can be specified at S_StartReset. |
|
NOTE:
Depending on the result of the risk analysis, optical, mechanical or inductive sensors such as reflection light sensors, mechanical or inductive switches can be used as muting sensors. Optical sensors serve as examples in the help information.
NOTE:
Only the material flow direction from muting sensors MutingSwitch11
MutingSwitch12 to muting sensors MutingSwitch21
MutingSwitch22 is described in the following. The function block also supports the opposite material flow direction from muting sensors MutingSwitch22
MutingSwitch21 to muting sensors MutingSwitch12
MutingSwitch11. The functional sequence remains identical.
The following graphic illustrates an application for the SF_MutingSeq function block.
Further Information
The entire muting operation is divided into different muting sequences. For more detailed information, see the functional description.
The material flow direction in the example shown is from left to right.
MS_11, MS_12: First sequential muting sensor pair, positioned before the safety-related equipment connected to the function block inputs MutingSwitch11 and MutingSwitch12 (the "yellow light beams" symbolize the detection area).
MS_21, MS_22: Second sequential muting sensor pair, positioned behind the safety-related equipment, connected to function block inputs MutingSwitch21 and MutingSwitch22.
S, R: Transmitter and receiver of the light grid (safety-related equipment)
T: Goods to be transported on an assembly conveyor
!: Zone of operation
Function block inputs
Click the corresponding hyperlinks to obtain detailed information on the items below.
|
Name |
Short description |
Value |
|
State-controlled input for activating the function block. Data type: BOOL Initial value: FALSE |
|
|
|
State-controlled input for the status of the safety-related equipment (e.g., light grid). Data type: SAFEBOOL Initial value: SAFEFALSE |
NOTE: The S_AOPD_Out output becomes SAFEFALSE when the muting operation is not active (S_MutingActive = SAFEFALSE).
|
|
|
State-controlled inputs for the muting sensors of the first sequential sensor pair. Data type: BOOL Initial value: FALSE For the material flow direction
|
|
|
|
State-controlled inputs for the muting sensors of the second sequential sensor pair. Data type: BOOL Initial value: FALSE For the material flow direction
|
|
|
|
State-controlled input for the feedback signal from the muting lamp. Data type: SAFEBOOL Initial value: SAFEFALSE |
|
|
|
Specification of the maximum permissible time for the entire muting operation. Data type: TIME Initial value: #0ms If the muting operation is not completed within this time, the S_AOPD_Out output is switched to the defined safe state SAFEFALSE (e.g., "switch off machine"). The following is valid for a material flow direction from left to right:
The following is valid for a material flow direction from right to left:
|
Minimum value: 0 s Maximum value: 600 s Enter a time value according to your risk analysis. Refer to the first hazard message below this table. |
|
|
State-controlled input for enabling the muting operation. Data type: BOOL Initial value: FALSE |
|
|
|
Specification of the start-up inhibit after the Safety Logic Controller has been started up or after the function block has been activated. Data type: SAFEBOOL Initial value: SAFEFALSE An active start-up inhibit must be removed manually by a positive signal edge at the Reset input. A deactivated start-up inhibit causes the S_AOPD_Out output to switch to SAFETRUE automatically when the function block is activated and the safety-related function is not requested. Refer to the second hazard message below this table. |
|
|
|
Edge-triggered input for the reset signal:
Refer to the third hazard message below this table. Data type: BOOL Initial value: FALSE NOTE: Resetting does not occur with a negative (falling) edge, as specified by standard EN ISO 13849-1, but with a positive (rising) edge. |
|
WARNING
NON-CONFORMANCE TO SAFETY FUNCTION REQUIREMENTS
Verify that the time value set at the time input corresponds to your risk analysis.
Be sure that your risk analysis includes an evaluation for incorrectly setting the time value at the time input.
Validate the overall safety-related function with regard to the set time value and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
WARNING
NON-CONFORMANCE TO SAFETY FUNCTION REQUIREMENTS
Be sure that your risk analysis includes an evaluation if the start-up inhibit is deactivated (S_StartReset = SAFETRUE).
Observe the regulations given by relevant sector standards regarding the start-up inhibit.
Verify that a suitable start-up inhibit is in place at another location or using other means if the start-up inhibit is deactivated by setting S_StartReset = SAFETRUE.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Resetting the function block by means of a positive signal edge at the Reset input can cause the S_AOPD_Out output to switch to SAFETRUE immediately (depending on the status of the other inputs).
WARNING
UNINTENDED START-UP
Include in your risk analysis the impact of the reset by means of a positive signal edge at the Reset input.
Make certain that appropriate procedures and measures (according to applicable sector standards) have been established to help avoid hazardous situations when resetting.
Do not enter the zone of operation when resetting.
Ensure that no other persons can access the zone of operation when resetting.
Use appropriate safety interlocks where personnel and/or equipment hazards exist.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Function block outputs
|
Name |
Short description |
Value |
|
Output for signaling "Function block activated / not activated". Data type: BOOL |
|
|
|
Output for enable signal of the function block. Data type: SAFEBOOL |
|
|
|
Output for the status of the muting operation. Data type: SAFEBOOL |
|
|
|
Output for error message. Data type: BOOL |
|
|
|
Output for diagnostic message. Data type: WORD |
Diagnostic message of the function block. The possible values are listed and described in the topic "Diagnostic codes". |
Signal sequence diagram
The signal sequence diagram shown below illustrates a muting operation (sequential muting with four sensors), using the example of an assembly conveyor that open into a zone of operation with a running machine (as represented in the graphic at the beginning of this topic).
The material flow direction of the conveyor is from left to right, i.e., both of the muting sensors connected to the function block inputs MutingSwitch11 and MutingSwitch12 are positioned one after another and on the same conveyor side before the safety-related equipment. The sensors connected to the function block inputs MutingSwitch21 and MutingSwitch22 are positioned behind the safety-related equipment (also sequential on the same side of the conveyor). This is represented in the graphic at the beginning of this topic.
Additional assumptions:
S_StartReset = SAFEFALSE: Start-up inhibit after the function block has been activated and the Safety Logic Controller has started up.
MutingEnable = TRUE (constant): No separate enable signal required for the muting operation.
NOTE:
The other signal sequence diagram can be taken into account.
NOTE:
The signal sequence diagrams in this documentation possibly omit particular diagnostic codes. For example, a diagnostic code is possibly not shown if the related function block state is a temporary transition state and only active for one cycle of the Safety Logic Controller.
Only typical input signal combinations are illustrated. Other signal combinations are possible.
|
0 |
The function block is not yet activated (Activate = FALSE). As a result, all outputs are FALSE or SAFEFALSE. |
|
1 |
After the function block has been activated by Activate = TRUE, the start-up inhibit is active at first. The S_AOPD_Out output therefore first remains SAFEFALSE. |
|
2 |
A positive signal edge at the Reset input resets the start-up inhibit. The S_AOPD_Out output switches to SAFETRUE immediately (normal operation) because
|
|
3 |
The first muting sensor of the first sequential sensor pair (before the safety-related equipment) at input MutingSwitch11 detects an object and switches to TRUE. The time measurement for the overall muting duration starts after this state change at MutingSwitch11. The maximum permissible period is specified at MaxMutingTime. |
|
4 |
The second muting sensor of the first sequential sensor pair also detects the object (the MutingSwitch12 input switches to TRUE). This meets the requirements for a valid muting sequence. The object is identified as permissible and the S_MutingActive output switches to SAFETRUE as a result: Muting is active. |
|
5 |
The object reaches the light grid: the S_AOPD_In input switches to SAFEFALSE ("light grid interrupted"). As muting is active (MutingSwitch11 and MutingSwitch12 are still TRUE), the machine may continue to run in the zone of operation: The S_AOPD_Out output remains SAFETRUE. |
|
6 |
The object reaches the first muting sensor of the second sequential sensor pair (behind the safety-related equipment): the MutingSwitch21 input switches to TRUE. The muting sequence is valid because both muting sensors of the first sensor pair are still TRUE. As a result, outputs S_AOPD_Out and S_MutingActive both remain SAFETRUE. The time measurement for the overall muting duration (timer MaxMutingTime) continues to run. |
|
7 |
The second muting sensor of the second sequential sensor pair also detects the object (the MutingSwitch22 input switches to TRUE). As TRUE signals are still also present at MutingSwitch11 and MutingSwitch12 and MutingSwitch21, the requirements for a valid muting sequence are met and muting remains active: S_AOPD_Out and S_MutingActive both remain SAFETRUE and timer MaxMutingTime continues to run. |
|
8 |
The object leaves the detection area of the first muting sensor before the safety-related equipment: The MutingSwitch11 input switches from TRUE to FALSE. This meets the requirements of a valid muting sequence, i.e., muting remains active. As a result, outputs S_AOPD_Out and S_MutingActive both remain SAFETRUE. The time measurement for the overall muting duration (timer MaxMutingTime) continues to run. |
|
9 |
The object leaves the detection area of the second muting sensor before the safety-related equipment: The MutingSwitch12 input switches from TRUE to FALSE. This meets the requirements of a valid muting sequence, i.e., muting remains active. As a result, outputs S_AOPD_Out and S_MutingActive both remain SAFETRUE. The time measurement for the overall muting duration (timer MaxMutingTime) continues to run. |
|
10 |
The object has passed the light grid (S_AOPD_In switches back to SAFETRUE). MutingSwitch21 and MutingSwitch22 are still TRUE. This meets the requirements of a valid muting sequence, i.e., muting remains active. As a result, outputs S_AOPD_Out and S_MutingActive both remain SAFETRUE. The time measurement for the overall muting duration (timer MaxMutingTime) continues to run. |
|
11 |
The object moves out of the detection area of the first muting sensor behind the safety-related equipment and toward the zone of operation: The MutingSwitch21 input switches to FALSE. If MutingSwitch21 switches to FALSE within the time set at MaxMutingTime, the muting operation has been completed successfully. S_MutingActive becomes SAFEFALSE and output S_AOPD_Out remains SAFETRUE. As the safety-related equipment has not detected an object and the muting operation has been completed within the specified time set at MaxMutingTime and the state change at MutingSwitch21 meets the requirements of a valid muting sequence, no error is reported (Error remains FALSE) and the S_AOPD_Out output remains SAFETRUE ("machine continues to run"). |
|
12 |
The MutingSwitch22 input also switches to FALSE and the safety-related equipment does not detect an object. The S_AOPD_Out output remains SAFETRUE as this conforms to a valid muting sequence. The muting operation is, therefore, completed successfully. |
Application example
The graphic below illustrates the connection of four muting sensors (B2, B3, B4, and B5) to the SF_MutingSeq function block. The muting sensors are arranged as two sequential sensor pairs with all sensors aligned identically and installed on the same side of the conveyor.
The material flow direction of the conveyor is from left to right, i.e., the muting sensor pair MutingSwitch11/MutingSwitch12 is positioned before the safety-related equipment and MutingSwitch21/MutingSwitch22 is behind the safety-related equipment (as represented in the graphic at the beginning of this topic).
Further Information
The description and notes for this application example can be taken into account.
NOTE:
The S_AOPD_Out enable output of the SF_MutingSeq function block is connected to an output terminal of the application via a global I/O variable or via other safety-related functions/function blocks.
|
B1 |
Two-channel light grid (B1S = optoelectronic transmitter, B1E = optoelectronic receiver) |
|
B2, B3 |
Optoelectronic muting sensors (first sequential sensor pair), each single-channel, positioned before the light grid |
|
B4, B5 |
Optoelectronic muting sensors (second sequential sensor pair), each single-channel, positioned behind the light grid |
|
P1 |
Muting lamp with single-channel feedback signal, monitored by safety logic |
|
S1 |
Reset button (single-channel) to reset function block errors and to remove the start-up inhibit |
|
|
See note above the illustration. |
Detailed information
Additional information is available in the following sections: