RAMP_INT (FB)

 

FUNCTION_BLOCK RAMP_INT

Limits the slope of a value to a certain value

The limitation of the slope is given by the maximum ascend ASCEND and the maximum descend DESCEND and a time base TIMEBASE defining the time for which ASCEND or DESCEND hold.

Note

It is not necessary to readjust the controller parameters (KP, TN, TV) if the cycle time changes.

Example

Hysteresis.png

InOut:

Scope

Name

Type

Comment

Input

IN

INT

Input value

ASCEND

INT

Limitation of acceleration: Maximum ascent per time base Example: ASCEND := 25 and TIMEBASE := T#1s => Maximum ascent of 25 increments per second

DESCEND

INT

Limitation of deceleration: Maximum descent per time base (DESCEND > 0) Example: DESCEND := 20 and TIMEBASE := T#500ms => Maximum ascent of 20 increments in 500 milliseconds

TIMEBASE

TIME

Reference for ASCEND/DESCEND :

t#0s : ASCEND/DESCEND defined per call

else : ASCEND/DESCEND defined per specified time

If TIMEBASE = t#0s, then the time base is equal to the task cycle time. In this case the limitation refers to a task cycle.

Usually this corresponds exactly to one call of the function block RAMP_INT.

Note

If the time base TIMEBASE is smaller than the task cycle time, then this will lead to a violation of the sampling theorem and might result in a loss of information in the output signal.

RESET

BOOL

Reset of the function block

TRUE: Stops the internal calculation and reinitializes the function block.

The last calculated output value in OUT is maintained in order to start the internal calculation with it at the next restart of the function block.

FALSE: Outputs the smoothed input signal at output OUT.

Output

OUT

INT

Function value with limited ramp The value gets stored internally and will be used for the calculation of the ascent and the descent of the input signal.