Function: This command establishes a brief connection to the hardware and determines the devices in the network. You can then adopt the devices found into the device tree of your project.
Call: Main menu Project , context menu of a device object in the device tree.
Requirement: The settings for communication with the control device are correct. The gateway and the PLC are running. The device supports the scan function.
The following devices provide the scan function: EtherCAT, EtherNet/IP (IEC), Sercos, CANopen, PROFINET, PROFIBUS DP.
Note
You can perform the scan immediately if the scan function is permanently implemented in the PLC. If scan function is located in a library, you must log in once in order to load the library to the controller.
The command refers to the master controller selected in the device tree. For example, an already inserted PROFINET IO controller can be selected and the command used to determine the I/O devices and I/O modules assigned to it.
After scanning, the dialog box Scan for Devices appears with the results.
Device name, Device type, Address, Station name, etc. |
Data about the scanned device depending on network type. When you change a value in the list of scanned devices, the value is shown in italics. This indicates that the new value has been changed in the editor in CODESYS, but not in the device. When you download the value to the device, it is shown normally. Value that indicate differences between the project and the scanned device are shown in orange. If several device descriptions are available for the scanned device, then the name is displayed in bold. The selection of the matching device description is resolved differently for different fieldbuses. Details can be found in the corresponding fieldbus sections. If a device description cannot be found, then the following message is shown: "Attention! The device was not found in the repository." Depending on the bus system, additional information is displayed, such as manufacturer number and product number. The device cannot be inserted into the project without the installed device description. |
Show differences to project |
|
Scan Devices |
Starts a new search. |
Copy all devices to project |
The device that is selected in the table is inserted into the device tree in the project. If nothing is selected, then all scanned devices are shown. |
Notice
If you insert devices, which are available in the device tree, to the device tree with Copy all devices to project, then the following should be noted. The data of the Process data and <...> I/O mapping tabs of the existing devices can be overwritten with the data of the recently inserted devices.
This part of the dialog is visible only when you select the Show differences to project option. Differences between the scanned and configured devices are color-coded. Devices in green are identical on both sides. Device in red are available only in the view of the scanned or configured devices. |
|
|
If you have selected a device in both views, then the scanned devices are inserted above the selected configured device. |
|
If you have selected a device in both views, then the scanned devices are inserted below the selected configured device. |
|
If you have selected a device in both views, then the configured devices are replaced by the selected scanned device. |
|
All scanned devices are copied to the project. |
|
Deletes the selected configure device. |
ID No. |
Display only when
|
Station name |
You can modify these entries or create them again before you accept the device and its settings into the configuration of the project. If you do not define an address, then the presets are used. The presets are defined in PNIO Controller Parameter. To determine the module structure of the station, it must possess a valid IP address (see setting the IP address with Set IP or Denominate). NOTICE: Each device must have received a station name because the name is required in network operation for certain functionalities. To declare the new name in the bus system, you must click the Denominate button for the selected device entry. |
IP address |
|
Subnet mask |
|
MAC address |
I M |
Use this command for retrieving the I&M data (identification and maintenance) of the device. The data is shown in the dialog IM data. |
Auto IP |
With this command, you automatically set a valid IP address within the network (network settings of the master) if the address scanned by the device is invalid. |
<-- |
Use this command for assigning the settings (Station name, IP address) from the configured device to the scanned device. |
--> |
Use this command for assigning the settings (Station name, IP address) from the scanned device to the configured device. |
Reset |
Resets the device settings to default values. |
Blink LED |
In the Found Devices view, you can identify a device by its hardware by selecting the entry in the dialog and clicking Blink LED. The device should respond with a flashing signal. |
Set Name+IP |
CODESYS attempts to set the station name and IP address that were specified for the selected slave. |
Show only unnamed stations |
|
Note
Please note the option of aligning the configuration settings of a PROFINET IO device with the settings of the corresponding hardware device.
I M version |
Implemented version of I&M functions |
Vendor ID |
ID of the manufacturer of the submodule |
Order ID |
Order number |
Serial Number |
Serial number of the submodule (unique production number) |
Hardware Revision |
Hardware version of the submodule |
Software Revision |
Software version of the submodule |
Location |
Location where the device is installed (for example, in a plant or production hall) |
Function |
Function or task of the submodule |
Date |
Day of installation or commissioning of the device or module Format compliant with ISO 8601: YYYY-MM DD HH:MM |
Description |
Any individual information |
Note
For some devices, the parameters Function, Location, Date, and Description can be modified.