TM5SDM4DTRFS Digital Mixed Safety Module
Module type/safety-related fields of application
Digital mixed safety-related module, 2 safety-related input channels, 2 pulse outputs, 24 VDC rated voltage, input filter configurable by software, 2 safety-related relay outputs, normally open contacts 48 VAC / 6 A, 24 VDC / 6 A.
Relay output protection: external 6 A gL/gG fuse; pulse outputs: thermal switch-off of individual channels if over-current or short-circuit occurs.
Schneider Electric safety-related modules can be used in safety-related applications according to:
EN ISO 13849, PL e
IEC 62061, SIL 3
IEC 61508, SIL 3
Group: Basic
Parameter: MinRequiredFWRev
Default value |
Basic Release |
Unit |
-/- |
Description |
This parameter is only relevant in case of implementing other firmware versions than the manufacturer-loaded version. To enter the operational state, the firmware version parameterized here or a newer version must be installed on the module.
The firmware version selected here is particularly important with regard to parameters or process data items that have been implemented with a particular firmware version. If the device you are currently working with has new parameters or process data items, the following applies: if MinRequiredFWRev is set to an incorrect value, either the SLC will not enter the operational run status or the new parameters/process data items will not be taken into account by the SLC. Refer to the hazard message below this table. Further Information Information on newly added parameters or process data items can be found in the Release Notes you received with the firmware package. The Release Notes also describe how to determine the firmware version that is currently installed on the safety-related device. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the selected value for MinRequiredFWRev corresponds to the firmware version installed on the safety-related devices involved.
Verify by means of functional tests that each newly implemented parameter or process data item of safety-related modules is taken into the account by the SLC where this is required by your safety-related application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Parameter: Optional
Default value |
No |
Unit |
-/- |
Description |
The module can be configured as optional using this parameter. Optional modules do not have to be available (physically present or communicative), i.e., if an optional module is unavailable, this is not signaled by the Safety LogicController. This parameter does not influence the module signal or status data. |
Possible values |
|
The Optional parameter is a mechanism to scale your safety-related system for various configurations of your machine design. However, it may be the case that the module(s) that you have designated as optional may be required in some of your alternative machine configurations.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify by means of functional tests that those modules that have the Optional parameter set to 'Yes' or 'Start-up' are available if and when required in alternative machine configurations.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Group: SafetyResponseTime
The safety response time is the time between the arrival of the sensor signal on the input channel of a safety-related input module and the shut-off signal at the output channel of a safety-related module. For further and detailed background information, refer to the topic "Safety Response Time".
The parameters in this group influence the safety response time of the Safety Logic Controller system. The parameters CommunicationWatchdog, MinDataTransportTime, and MaxDataTransportTime in this group are only applied to the module if ManualConfiguration is set to 'Yes'.
Parameter: ManualConfiguration
Default value |
No |
Unit |
-/- |
Description |
Specifies whether the module uses its safety response time-relevant parameters (CommunicationWatchdog, MinDataTransportTime, and MaxDataTransportTime) or the values specified in the 'SafetyResponseTimeDefaults' parameter group of the Safety Logic Controller. Managing parameters per module optimizes the system to application-specific requirements regarding the safety response time. |
Parameter value |
|
Parameter: MinDataTransportTime
Default value |
12 |
Value range Step size |
12...500 1 |
Unit |
100 µs |
Description |
Defines the minimum time that is required to transmit a data telegram from a producer to a consumer. If a telegram is received earlier (by the consumer) than specified by this parameter value, communication is considered as invalid. EcoStruxure Machine Expert - Safety provides a calculator dialog to determine this parameter value. Term definition and background information According to the openSAFETY specification, devices (safety-related I/O modules as well as the Safety Logic Controller) communicate by sending and receiving cyclic data, referred to as openSAFETY telegrams. A telegram generating (sending) device is designated as producer, a receiving device is a consumer. Each telegram includes a time stamp for time validation of the communication. On receipt of a telegram, the consumer compares this time stamp with the current time. If the schedule is kept, the communication is considered as valid. If a telegram is received earlier than defined by this parameter, communication is considered as invalid and is not further processed. The 'SafeModuleOK' process data item also becomes SAFEFALSE indicating that the safety-related communication of the module is no longer valid. The implications for the rest of the safety-related systems depend on the defined safety-related function. |
Value calculation |
How to calculate the module-specific MinDataTransportTime value
|
Practical values |
Entering the MinDataTransportTime value calculated in EcoStruxure Machine Expert - Safety results in a stable running system. |
Parameter: MaxDataTransportTime
Default value |
200 |
Value range Step size |
12...65,000 1 |
Unit |
100 µs |
Description |
Defines the maximum time that is allowed to transmit a data telegram from a producer to a consumer. If a telegram is received later (by the consumer) than specified by this parameter value, communication is considered as invalid. EcoStruxure Machine Expert - Safety provides a calculator dialog to determine this parameter value. NOTE: The parameter value influences the safety response time calculated by EcoStruxure Machine Expert - Safety. Term definition and background information According to the openSAFETY specification, devices (safety-related I/O modules as well as the Safety Logic Controller) communicate by sending and receiving cyclic data, referred to as openSAFETY telegrams. A telegram generating (sending) device is designated as producer, a receiving device is a consumer. Each telegram includes a time stamp for time validation of the communication. On receipt of a telegram, the consumer compares this time stamp with the current time. If the schedule is kept, the communication is considered as valid. If a telegram is received later than defined by this parameter, communication is considered as invalid and is not further processed. The implications for the rest of the safety-related systems depend on the defined safety-related function. |
Value calculation |
How to calculate the module-specific MaxDataTransportTime value
|
Practical values |
Entering the MaxDataTransportTime value calculated in EcoStruxure Machine Expert - Safety results in a stable running system. |
Parameter: CommunicationWatchdog
Default value |
200 |
Value range Step size |
1...65,535 1 |
Unit |
100 µs |
Description |
Defines the maximum time period within which a consumer must receive a valid data telegram from a producer in order to consider the safety-related communication as valid and continue the application. The parameter sets a watchdog timer which then monitors whether a consumer receives telegrams from a producer in time. If the watchdog expires, communication is considered as invalid. EcoStruxure Machine Expert - Safety provides a calculator to determine this parameter value. NOTE: The parameter value influences the safety response time calculated by EcoStruxure Machine Expert - Safety. Term definition and background information According to the openSAFETY specification, devices (safety-related I/O modules as well as the Safety Logic Controller) communicate by sending and receiving cyclic data, referred to as openSAFETY telegrams. A telegram generating (sending) device is designated as producer, a receiving device is a consumer. The CommunicationWatchdog value physically depends on the transport time needed for the telegram to be transmitted from a producer to a consumer and influences the worst case response time of the system. The calculated parameter value therefore depends on the MaxDataTransportTime parameter value. If the consumer receives the telegram in time (communication watchdog is not yet expired and the transmission time is within the period specified by the parameters MinDataTransportTime and MaxDataTransportTime), the watchdog timer is restarted and communication is considered as valid. The time stamp contained in the received telegram is not evaluated, only the receipt of a valid telegram is relevant. If no telegram is received (due to delay or loss) and the communication watchdog expires in the consumer, the module is set to the defined safe state. The 'SafeModuleOK' process data item also becomes SAFEFALSE indicating that the safety-related communication of the module is no longer valid. |
Value calculation |
How to calculate the module-specific CommunicationWatchdog value
|
Practical values |
For the CommunicationWatchdog value which you must enter in the parameter grid ('Devices' window), the following applies:
|
Group: SafeDigitalInput01 and SafeDigitalInput02
Parameter: PulseSource
This parameter is not available for the input channel 1 (parameter group SafeDigitalInput01) of the module. |
|
Default value |
default |
Unit |
-/- |
Description |
Specifies the source of the pulse input: By setting another value than 'Default', the current channel can be operated with the pulse signal output of another channel of the same module. |
Possible values |
The drop-down list offers the available pulse outputs of the same module. Set to 'default', the channel uses its own pulse signal. NOTE: When setting a value other than 'default', the PulseMode parameter of the respective channel must be set to 'internal'. Multi-channel switches (mode selector switches, switching devices with "shift key" capability) can be connected to multiple safety-related digital input modules. In this case, the following rules apply:
|
When using the same pulse signals for different input channels, the pulse signals must be isolated from one another. Otherwise, damage to the cables may cause cross circuit errors that are not detected by the module.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that signal lines that use the same pulse signals are routed in different cables isolated from each other or that other suitable error preventing measures (according to IEC 13849-2) have been taken to detect cross circuits in pulse signal lines.
For adjacent input channels that use the same pulse signal, thoroughly verify that the inputs are not connected inadvertently by improper wiring.
Validate the physical wiring of your safety-related architecture and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
The possible pulse source settings for the input channels as well as the default pulse source are shown in the following table. The entry "-" means that this pulse source cannot be used for the input channel.
Parameter: PulseMode
Default value |
Internal |
Unit |
-/- |
Description |
Specifies the pulse mode of the input channel. |
Possible values |
NOTE: Also observe the safety-related notes and hazard messages in the device manual. |
1 |
With the configuration 'PulseMode = no Pulse', the module itself is not able to detect wiring errors. Internal errors, however, are still detected. All errors resulting from incorrect, damaged or disconnected wiring must be handled through supplementary measures in accordance with EN ISO 13849-2:2012 or by the connected device. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Validate the wiring of your safety-related application and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Parameter: FilterOff
Default value |
0 |
Value range Step size |
0...500,000 1 |
Unit |
µs |
Description |
Configures a switch-off filter for the channel to remove potentially disruptive "low phases" on the input signal. Configuring a switch-off filter increases the data processing time of the safety-related module and therefore also the safety response time. Refer to the first hazard message below this table. Configuring a switch-off filter causes input signals with a "low phase" shorter than the switch-off filter to be filtered out. If this results in unintended operation of your equipment, the FilterOff parameter must be set to 0. Extending the "low phase" with a switch-on filter (FilterOn parameter) is not possible in these cases. Refer to the second hazard message below this table. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Recalculate and validate the safety response time after modifying the FilterOff parameter.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the value set for the FilterOff parameter is less than the shortest "low-phase" of the input signal and therefore no input signals are filtered out.
Disable the switch-off filter by setting the FilterOff parameter to 0 if a value greater than 0 causes unintended operation of your equipment.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
Parameter: FilterOn
Default value |
150,000 |
Value range Step size |
0...500,000 1 |
Unit |
µs |
Description |
Sets the switch-on filter for the channel. Input signals can be debounced with the switch-on filter. Furthermore, using this function, you can extend a module switch-off signal that would otherwise be too short. Input signals with a "low phase" shorter than the safety response time can be lost. Such signals should be extended accordingly using the FilterOn parameter ('switch-on filter') on the input module. |
Parameter: DiscrepancyTime
Default value |
0 |
Value range Step size |
0...500,000 1 |
Unit |
µs |
Description |
This parameter is only available for odd-numbered channels. If set, it combines the current channel with the next channel for two-channel evaluation. (Setting channel n combines n and n+1.) The value specifies the maximum time interval for the two-channel evaluation, during which the status of both physical individual channels may be undefined without triggering an error. Whether the channels are monitored for antivalence or equivalence depends on the used process data items: the module provides SafeEquivalentInputs as well as SafeAntivalentInputs. Violation of the DiscrepancyTime can be monitored by evaluating the SafeEquivalentOK or SafeAntivalentOK process data items for the module in the safety-related application. |
Group: SafeDigitalOutput01, SafeDigitalOutput02, SafeDigitalOutput0102
Parameter: AutoRestart
Default value |
No |
Unit |
-/- |
Description |
Activates or deactivates the automatic restart of the output of the module. |
Possible values |
NOTE: The following applies independently of the automatic restart configuration (both settings): After a channel error has been detected in the module (and the source of the error has been removed or otherwise mitigated), the affected output must be deactivated and activated again by means of a positive edge of the release signal. |
NOTE:
Configuring an automatic restart can result in unintended implications for the safety-related system. It may be necessary to implement additional measures to avoid unintended consequences.
WARNING
UNINTENDED START-UP
Be sure that your risk analysis includes an evaluation for an automatic restart of the output of the module.
Make certain that appropriate procedures and measures (according to applicable sector standards) have been taken to help avoid hazardous situations in case of an automatic restart.
Use appropriate safety interlocks where personnel and/or equipment hazards exist.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
NOTE:
The SafeDigitalOutput0102 parameter defines the behavior of both outputs SafeDigitalOutput01 and SafeDigitalOutput02 if they are connected in series.
The serial connection of both outputs is the prerequisite for achieving a higher level of functional safety (SIL 3 according to IEC 62061, for example).
The SafeDigitalOutput0102 process data item of the module causes a switch-on sequence that switches on relay 2 with a 20 ms delay. Refer to the device manual for more details.
Process data items of the module
Purpose and use of process data items
Each module provides process data items (signals). Process data items can be:
I/O signals delivered from or written to a module terminal.
diagnostic signals for evaluating the status of input/output channels or the entire module.
control signals, for example, for enabling a channel or adjusting the module.
The available process data items of a module are listed under the module node in the tree on the left of the 'Devices' window. To display and use the process data items, expand the module node in the tree by clicking the '+' symbol.
Example
The module with the ID SL1.SM3 provides (among others) the diagnostic signal SafeModuleOK and the input signal SafeDigitalInput01.
From the devices tree, process data items can be inserted into the safety-related FBD/LD code by drag & drop (see following procedure). On insertion into the code, a standard (non-safety-related) or safety-related global variable is created (depending on the data type of the process data item).
Procedure: How to insert process data items into the code
Open the code worksheet where you want to insert the process data item and create/use the global variable assigned to it.
In the 'Devices' window, open the devices tree on the left and expand the module (tree node) which contains the process data item to be used.
Drag the process data item into the code worksheet. When releasing the mouse button, the 'Variable' dialog appears.
To insert a Boolean variable as a contact into the graphical code, hold the <CTRL> key down when releasing the mouse button after dragging the variable from the device terminal grid into the code worksheet.
In the 'Variable' dialog, a default name is proposed which is derived from the process data item name. Accept the proposed name, select an existing global variable, or declare a new global variable by entering a new 'Name', defining the 'Data Type' and selecting a 'Group'.
Confirm the 'Variable' dialog by clicking 'OK'.
The rectangle shape of the variable is now added to the cursor. It can be dropped at the desired position with a click. You can directly connect the variable to another object (e.g., a formal parameter as shown in the following example) or dropped at any free position.
Data direction depends on the signal type
Input signals can only be read and output signals can be written by the safety-related application.
Diagnostic signals can be used to evaluate and monitor the status of the safety-related module or individual I/O channels, for example. Therefore, global variables created for and assigned to diagnostic signals can be read by the application.
Control signals can be used to enable the module operation or to adjust/adapt the module for the present use case (for example, by setting a measurement range or a particular module behavior). The global variables created for and assigned to control signals can be written by the application, thus controlling the module.
Representation of the process data items in the devices tree:
Icon |
Signal type |
Access type |
![]() |
Safety-related input signal or diagnostic signal. |
read |
![]() |
Non-safety-related input signal (only available for the Safety Logic Controller). |
read |
![]() |
Non-safety-related output signal (only available for the Safety Logic Controller) or control signal. |
write |
![]() |
Safety-related output or control signal. |
write |
NOTE:
If a standard (non-safety-related) signal is connected to a physical input or output, the data type of the corresponding global variable must be modified from safety-related to standard (e.g., from SAFEBOOL to BOOL) to rule out an incorrect use of the signal in the code. The same applies if a safety-related signal is used only as standard signal in the code. Modifying the data type can either be done in the appropriate variables worksheet or using type converter functions.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify the impact of standard (non-safety-related) signals on safety-related outputs.
Verify that "standard to safety-related" converters are used correctly in the code.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
In the following, the I/O, diagnostic and control signals of the present module are listed and described in the order they are listed in the devices tree.
SafeModuleOK
Description |
Indicates the status of the communication between the safety-related module and the Safety Logic Controller and therefore, from safety-related application perspective, the module status itself. |
Signal type |
Diagnostic |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
SAFEFALSE:
SAFETRUE:
|
Mandatory assignment validation for the SafeModuleOK data item:
The verification/validation of the assignment of each process data item to a global I/O variable is mandatory. This particularly applies to the SafeModuleOK process data item which is available for each safety-related module and indicates its status. As the SafeModuleOK data item cannot be written to, e.g., by applying a signal to a module input, the module to be verified must be physically removed from the TM5 bus. As a result, SafeModuleOK switches to SAFEFALSE and the assigned global I/O variable must follow. For further information on the steps to remove and reinsert a module, refer to the user manual of the module.
WARNING
UNINTENDED EQUIPMENT OPERATION
Physically remove each safety-related module from the TM5 bus in order to test for SafeModuleOK.
Verify that the global I/O variable assigned to the SafeModuleOK process data item of the removed safety-related module switches to SAFEFALSE.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeDigitalInputxx
Description |
Digital input signal from the single-channel command device or sensor connected to the module. xx specifies the channel number of the module. NOTE: For equivalence or antivalence monitoring at an input channel pair, use the respective combined signal xxyy instead of this single channel. The validity of this input signal is confirmed by the related diagnostic signal SafeChannelOKxx and/or SafeInputOKxx (depending on the module). Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeDigitalInputxx signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeDigitalInputxx value. In this case, the SafeDigitalInputxx signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. |
Signal type |
I/O signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
If SafeModuleOK = SAFETRUE and the channel-related diagnostic signal(s) SafeChannelOKxx and/or SafeInputOKxx = SAFETRUE (depending on the module), the following applies: SAFETRUE: Digital input channel is set to true. SAFEFALSE: Digital input channel is set to false. |
Relevant module parameters |
In the parameter group with the same channel number xx:
The related parameter descriptions can be found above in this topic. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeDigitalInputxx signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeEquivalentInputxxyy
Description |
Signal resulting from the equivalence monitoring of the input signals specified with xx (first channel) and yy (second channel). Both channels xx and yy must be connected to the same contact types (both NC or both NO) of the two-channel command device or sensor. Equivalence between the involved channels must be established before the interval specified with the DiscrepancyTime parameter has elapsed. Otherwise, the related diagnostic signal SafeEquivalentOKxxyy switches to SAFEFALSE and the channel is disabled. The validity of this input signal is confirmed by the related diagnostic signal SafeEquivalentOKxxyy. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeEquivalentInputxxyy signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeEquivalentInputxxyy value. In this case, the SafeEquivalentInputxxyy signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. NOTE: The signals SafeAntivalentInputxxyy and SafeEquivalentInputxxyy cannot be used at the same time. When using the SafeAntivalentInputxxyy or SafeEquivalentInputxxyy signal, the involved individual inputs (SafeDigitalInputxx and SafeDigitalInputyy) cannot be used at the same time. |
Signal type |
I/O signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
If SafeModuleOK = SAFETRUE and SafeEquivalentOKxxyy = SAFETRUE, the following applies: SAFEFALSE: at least one of the channels xx or yy is SAFEFALSE or the set discrepancy time has elapsed without equivalent signals SAFETRUE: channel xx = SAFETRUE and channel yy = SAFETRUE |
Relevant module parameters |
In the parameter groups of the channels involved (xx and yy):
The related parameter descriptions can be found above in this topic. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeEquivalentInputxxyy signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeAntivalentInputxxyy
Description |
Signal resulting from the antivalence monitoring of the input signals specified with xx (first channel) and yy (second channel). The channels xx and yy must be connected to opposing contact types of the two-channel command device or sensor, for example, channel xx to an NC contact and channel yy to an NO contact or vice versa. Antivalence between the involved channels must be established before the interval specified with the DiscrepancyTime parameter has elapsed. Otherwise, the related diagnostic signal SafeAntivalentOKxxyy switches to SAFEFALSE and the channel is disabled. The validity of this input signal is confirmed by the related diagnostic signal SafeAntivalentOKxxyy. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeAntivalentInputxxyy signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeAntivalentInputxxyy value. In this case, the SafeAntivalentInputxxyy signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. NOTE: The signals SafeAntivalentInputxxyy and SafeEquivalentInputxxyy cannot be used at the same time. When using the SafeAntivalentInputxxyy or SafeEquivalentInputxxyy signal, the involved individual inputs (SafeDigitalInputxx and SafeDigitalInputyy) cannot be used at the same time. |
Signal type |
I/O signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
If SafeModuleOK = SAFETRUE and SafeAntivalentOKxxyy = SAFETRUE, the following applies: SAFEFALSE: channel xx = SAFEFALSE and/or channel yy = SAFETRUE or the set discrepancy time has elapsed without antivalent signals. SAFETRUE: channel xx = SAFETRUE and channel yy = SAFEFALSE |
Relevant module parameters |
In the parameter groups of the channels involved (xx and yy):
The related parameter descriptions can be found above in this topic. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeAntivalentInputxxyy signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeInputOKxx
Description |
Diagnostic signal which indicates the status of the safety-related digital input channel. xx specifies the channel number. This diagnostic signal confirms the validity of the SafeDigitalInputxx signal. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeDigitalInputxx signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeDigitalInputxx value. In this case, the SafeDigitalInputxx signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. NOTE: To detect error status conditions of modules/channels within your application, diagnostic signals must be evaluated in the safety-related code. A programming example and further information can be found in the topic "Monitoring/evaluating diagnostic information of the machine". |
Signal type |
Diagnostic signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
SAFEFALSE:
SAFETRUE:
NOTE: Also observe the respective LED indicator(s) of the affected modules for the error indication. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeDigitalInputxx signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeEquivalentOKxxyy
Description |
Diagnostic signal which indicates the status of the equivalence signal evaluation at the safety-related digital input channel pair xx and yy. This diagnostic signal confirms the validity of the SafeEquivalentInputxxyy signal. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeEquivalentInputxxyy signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeEquivalentInputxxyy value. In this case, the SafeEquivalentInputxxyy signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. NOTE: To detect error status conditions of modules/channels within your application, diagnostic signals must be evaluated in the safety-related code. A programming example and further information can be found in the topic "Monitoring/evaluating diagnostic information of the machine". |
Signal type |
Diagnostic signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
SAFEFALSE:
SAFETRUE:
NOTE: Also observe the respective LED indicator(s) of the affected modules for the error indication. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeEquivalentInputxxyy signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeAntivalentOKxxyy
Description |
Diagnostic signal which indicates the status of the antivalence signal evaluation at the safety-related digital input channel pair xx and yy. This diagnostic signal confirms the validity of the SafeAntivalentInputxxyy signal. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeAntivalentInputxxyy signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeAntivalentInputxxyy value. In this case, the SafeAntivalentInputxxyy signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. NOTE: To detect error status conditions of modules/channels within your application, diagnostic signals must be evaluated in the safety-related code. A programming example and further information can be found in the topic "Monitoring/evaluating diagnostic information of the machine". |
Signal type |
Diagnostic signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
SAFEFALSE:
SAFETRUE:
NOTE: Also observe the respective LED indicator(s) of the affected modules for the error indication. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeAntivalentInputxxyy signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeDigitalOutputxx
Description |
Safety-related enable signal of the module, channel xx. NOTE: The single-channel signals SafeDigitalOutputxx cannot be used at the same time with the combined enable signal SafeDigitalOutputxxyy of the module. General Information In general, safety-related outputs can only be written by the Safety Logic Controller (SLC). Depending on the setting in the respective safety-related TM5/TM7 output module, the non-safety-related controller must additionally enable the safety-related output (acknowledge the safety-related signal). For that purpose, the 'User Parameters' editor of the SDO module in Logic Builder provides one CentralControl_DigitalOutputs_xx parameter per output channel. To open this editor, go to Logic Builder, double-click the SDO module in the 'Devices' tree, and click the tab 'User Parameters'. The CentralControl_DigitalOutputs_xx parameter has two possible parameter values:
The enable signal may only control the process directly if it does not adversely affect the safety-related function. Refer to the first hazard message below this table. NOTE: In the EcoStruxure Machine Expert - Safety 'Devices' window, the column 'LogicBuilder Variable' displays the name of the variable which has been mapped to the enable signal in the 'TM5 Module I/O Mapping' editor in Logic Builder. This representation must not be misinterpreted: Although the enable signal ('ChannelName'), the safety-related 'Variable' name, and the LogicBuilder variable are displayed in one row, the LogicBuilder variable cannot write the safety-related output. The LogicBuilder variable only agrees to the activation of the output. The physical activation of the output, however, can exclusively be initiated by the SLC. Confirmation of validity The validity of this output signal is confirmed by the related diagnostic signal SafeOutputOKxx. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeDigitalOutputxx signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeDigitalOutputxx value. In this case, the SafeDigitalOutputxx signal must not be further used, processed, or evaluated in the safety-related application. Refer to the second hazard message below this table. Further Information Refer to the topic "Monitoring/evaluating diagnostic information of the machine" for further information. Restart inhibit active When a restart inhibit is active for channel xx (parameter 'AutoStart = No'), the safety-related output remains in the defined safe state after removing the safety request, or, in case of a module error, the cause of the error. This is to avoid an inadvertent machine/system restart. If the restart inhibit has been specified, a positive edge at the relating ReleaseOutputxx signal (see description below) is required to remove the inhibit and enable the machine/system to function. |
Signal type |
I/O signal |
Data type |
SAFEBOOL |
Access type |
Variable can be written by the safety-related application. The effect of the variable value depends on the setting of the CentralControl_DigitalOutput_xx module parameter in the EcoStruxure Machine Expert application (see "Description" above). |
Possible values |
SAFETRUE:
SAFEFALSE:
|
Relevant module parameters |
In the parameter group with the same channel number xx:
The related parameter descriptions can be found above in this topic. In the EcoStruxure Machine Expert application, 'User Parameters' of the output module:
|
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the enable signal only controls the process directly if it does not adversely affect the safety-related function.
Validate the overall safety-related function, including the start-up behavior of the process, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeDigitalOutputxx signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeDigitalOutputxxyy
Description |
Safety-related two-channel enable signal of the module, i.e., the combination of the single channels xx and yy. The enable signal may only control the process directly if it does not adversely affect the safety-related function. Refer to the first hazard message below this table. The validity of this output signal is confirmed by the related diagnostic signal SafeOutputOKxxyy. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeDigitalOutputxxyy signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeDigitalOutputxxyy value. In this case, the SafeDigitalOutputxxyy signal must not be further used, processed, or evaluated in the safety-related application. Refer to the second hazard message below this table. Further Information Refer to the topic "Monitoring/evaluating diagnostic information of the machine" for further information. When a restart inhibit is active for channel xxyy (parameter 'AutoStart = No'), the safety-related output remains in the defined safe state after removing the safety request, or, in case of a module error, the cause of the error. This is to avoid an inadvertent machine/system restart. If the restart inhibit has been specified, a positive edge at the relating ReleaseOutputxxyy signal (see description below) is required to remove the inhibit and enable the machine/system to function. NOTE: The single-channel signals SafeDigitalOutputxx cannot be used at the same time with the combined enable signal SafeDigitalOutputxxyy of the module. |
Signal type |
I/O signal |
Data type |
SAFEBOOL |
Access type |
Variable can be written by the safety-related application depending on the user parameters in the EcoStruxure Machine Expert application "CentralControl_DigitalOutput_xx" |
Possible values |
SAFETRUE:
SAFEFALSE:
|
Relevant module parameters |
In the parameter group with the same channel number xxyy:
The related parameter descriptions can be found above in this topic. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the enable signal only controls the process directly if it does not adversely affect the safety-related function.
Validate the overall safety-related function, including the start-up behavior of the process, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeDigitalOutputxxyy signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
SafeOutputOKxx
Description |
Diagnostic signal which indicates the status of the safety-related output channel (enable signal). xx specifies the output number. This diagnostic signal confirms the validity of the SafeOutputxx signal. Depending on the results of the risk analysis you carried out for your application, the diagnostic signal must be evaluated each time the SafeOutputxx signal is used in the safety-related application. The value SAFEFALSE of the diagnostic signal indicates an invalid SafeOutputxx value. In this case, the SafeOutputxx signal must not be further used, processed, or evaluated in the safety-related application. Refer to the hazard message below this table. NOTE: To detect error status conditions of modules/channels within your application, diagnostic signals must be evaluated in the safety-related code. A programming example and further information can be found in the topic "Monitoring/evaluating diagnostic information of the machine". |
Signal type |
Diagnostic signal |
Data type |
SAFEBOOL |
Access type |
Variable can be read by the safety-related application |
Possible values |
SAFEFALSE:
SAFETRUE:
NOTE: Also observe the respective LED indicator(s) of the affected modules for the error indication. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Verify that the SafeOutputxx signal is only used in the safety-related application as long as the related diagnostic signals are SAFETRUE if demanded by the results of your risk analysis.
Validate the overall safety-related function with respect to the processing of input values, and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.
ReleaseOutputxx and ReleaseOutputxxyy
Description |
ReleaseOutputxx is the release signal for the single-channel enable signal SafeOutputxx. ReleaseOutputxxyy is the release signal for the two-channel enable signal SafeOutputxxyy, i.e., the combination of the output channels xx and yy. When a restart inhibit is active for channel xx/xxyy (parameter 'AutoStart = No'), the safety-related output remains in the defined safe state after removing the safety request, or, in case of a module error, the cause of the error. This is to avoid an inadvertent machine/system restart. If the restart inhibit has been specified, a positive edge of the respective release signal is required to remove the inhibit and enable the machine/system to function. Resetting a diagnostic state and setting an output must not result in any hazards. In case of any doubt, reset the entire system instead of the single channel. Refer to the hazard message below this table. Further Information Refer to the topic "Monitoring/evaluating diagnostic information of the machine" for further information and an application example. NOTE: If the safety-related module enters the defined safe state and SafeModuleOK = SAFEFALSE, the ReleaseOutputxx/xxyy signal cannot be used to release the channel. Instead, the entire module must be restarted. Example: if input values exceed the allowed electrical maximum values as specified in the technical data of the device, the module must be restarted. |
Signal type |
Control signal |
Data type |
SAFEBOOL |
Access type |
Variable can be written by the safety-related application |
Possible values |
|
Relevant module parameters |
In the parameter groups with the same channel number xx/xxyy:
The related parameter descriptions can be found above in this topic. |
WARNING
UNINTENDED EQUIPMENT OPERATION
Include in your risk analysis the impact of resetting the diagnostic state of a module or input/output channel and setting an output channel.
Use appropriate safety interlocks where personnel and/or equipment hazards exist.
Validate the overall safety-related function and thoroughly test the application.
Failure to follow these instructions can result in death, serious injury, or equipment damage.