FUNCTION_BLOCK MC_TouchProbe
This function block is designed for recording an axis position when a trigger event is raised.
Note
The function block is intended for single shot operation, that is, only the first event following on a rising edge of Execute is valid for recording. Further events will be ignored.
One function block instance should represent exactly one probing command.
Example
Timing and TouchProbe
Example
Defining a window, where trigger events are accepted (for modulo axes).
InOut:
|
Scope |
Name |
Type |
Initial |
Comment |
|
Inout |
Axis |
Reference to axis, the position of which is to be recorded at a defined event at the trigger input. |
||
|
TriggerInput |
Reference to trigger signal source |
|||
|
Input |
Execute |
BOOL |
FALSE |
Rising edge: Starts the execution of the function block. |
|
WindowOnly |
BOOL |
FALSE |
TRUE: Trigger events will be accepted only within the specified window (definition hereunder). |
|
|
FirstPosition |
LREAL |
0 |
Start position from whereon (in positive direction) trigger events will be accepted (in technical units [u]). |
|
|
LastPosition |
LREAL |
0 |
End position up to which trigger events will be accepted (in technical units [u]). |
|
|
Output |
Done |
BOOL |
FALSE |
TRUE: Trigger event has been recorded. |
|
Busy |
BOOL |
FALSE |
TRUE: Execution of function block has not been finished yet. |
|
|
Error |
BOOL |
FALSE |
TRUE: Error occurred within the function block. |
|
|
ErrorID |
SMC_ERROR |
0 |
Error identification |
|
|
RecordedPosition |
LREAL |
0 |
Position, where trigger event has occurred (in technical units [u]). |
|
|
CommandAborted |
BOOL |
TRUE: Command has been aborted by another command. |