FUNCTION_BLOCK SMC_BlockSearch
This function block shortens the path from start up to the position that is stored in SMC_BlockSearchPos . From this position, the original path is put on. SMC_BlockSearch runs in the context of the path preprocessing and is inserted typically in the data flow before SMC_CheckVelocities .
Note
SMC_BlockSearch requires the position values from SMC_BlockSearchPos , that must be executed previously.
InOut:
|
Scope |
Name |
Type |
Initial |
Comment |
|
Inout |
ePos |
Position information. Requires connection to output ePos of SMC_BlockSearchSavePos |
||
|
Input |
bExecute |
BOOL |
FALSE |
Risign edge: Enables the function block |
|
bAbort |
BOOL |
FALSE |
TRUE: Aborts the processing of the function block |
|
|
bAppend |
BOOL |
FALSE |
FALSE: Starts emptying poqDataOut on a rising edge at bExecute |
|
|
poqDataIn |
POINTER TO SMC_OUTQUEUE |
NULL |
Pointer to data of structure SMC_OUTQUEUE containing the path objects of typ SMC_GEOINFO, that are interpolated. |
|
|
bStartFromSavedPos |
BOOL |
TRUE: Enables the function block to shorten the path from start up to the position, that is stored in SMC_BlockSearchPos . FALSE: Disables the function block |
||
|
nSizeOutQueue |
UDINT |
0 |
Size in bytes of the data buffer pbyBufferOutQueue, in which the path elements are copied. If the value is set, it may not be changed except after a reset. |
|
|
pbyBufferOutQueue |
POINTER TO ARRAY [0..0] OF SMC_GEOINFO |
NULL |
Pointer to the first byte of the storage area created for the path elements. If the value is set, it may not be changed except after a reset. |
|
|
Output |
bDone |
BOOL |
FALSE |
TRUE: input date from poqDataIn have been precessed fully. After that, the function block performs no action until a reset is detected. When bExecute is set to FALSE, bDone is reset to FALSE. |
|
bBusy |
BOOL |
FALSE |
TRUE: Function block in execution |
|
|
bError |
BOOL |
FALSE |
TRUE: Error has occurred |
|
|
wErrorID |
SMC_ERROR |
0 |
Error identification Possible values
|
|
|
poqDataOut |
POINTER TO SMC_OUTQUEUE |
NULL |
Pointer to data of structure SMC_OUTQUEUE containing the path elements of type SMC_GEOINFO that have been processed |