SMC_ExtendedVelocityChecks (FB)
FUNCTION_BLOCK SMC_ExtendedVelocityChecks
This function reduces the velocity, acceleration and deceleration of the path so that the resulting velocity, acceleration and deceleration values for the additional axes (Z, P, Q, U, V, W and additionally Z for the 2D mode) do not exceed the values set in F<Axis> and E<Axis> .
These limits are typically defined in the G-code by using the G-code words FZ, FP, FQ, FU, FV, FW and EZ, EP, EQ, EU, EV, EW.
FF0, FZ0, FP0, ..., FW0 reset the velocity limit of the associated axis. EF0, EZ0, EP0, ..., EW0 reset the limitation of acceleration or deceleration of the associated axis. FZ and EZ are only valid in the 2D-mode.
Additionally there are EA, EB, EC and FA, FB and FC associated to A, B and C which overlay the axis U, V and W.
Example
Acceleration and deceleration values are set for additional axis for limit them. In sentence N0, the acceleration of additional axis P is limited to 10, the deceleration is limited to 13. In sentence N1, the limitations on additional axis P are reset again (EP0).
G-Code:
N0 G1 X100 EP10 EP-13 P100
N1 G1 X200 EP0 P0
E<axis>/F<axis>
The following code is used to define velocity/acceleration/deceleration of a additional axes <axis> by E<axis>/F<axis>.
G-Code
N20 M9
N030 F10 E40.0 E-40.0
N040 M8
N050 G92 X0.0 Y0.0 Z570.0 U35.0 V225.0 W20.0 P382.0 (Starting position)
N060 G1 X0.0 Y0.0 Z570.0 U35.0 V225.0 W20.0 P382.0
N230 G0 X0.0 F200.0 E200.0 E-200.0
N240 M7
N250 F50.0 E40.0 E-40.0
N260 G0 U100.0 V158.0 W100.0 P260.0 Y100.0 Z400.0 F50.0
N270 G0 V125.0 P260.0 Z400.0 FV1.25 EV500 EV-500 (additional axis V is set)
N280 G0 V170.0 P260.0 Z400.0 FV50.0
N285 G0 V170.0 P260.0 Z400.0 FP100.0 EP500 EP-500 (additional axis P is set)
N290 G0 X0.0 F200.0 E200.0 E-200.0
N300 M7
N310 F50.0 E40.0 E-40.0
N320 G0 U100.0 V158.0 W100.0 P260.0 Y100.0 Z400.0 F50.0
N330 G0 V125.0 P260.0 Z400.0 F1.25
N340 G0 V170.0 P260.0 Z400.0 F50.0
N350 M8
InOut:
|
Scope |
Name |
Type |
Initial |
Comment |
|
Input |
bExecute |
BOOL |
FALSE |
Execution starts on the rising edge. |
|
bAbort |
BOOL |
FALSE |
If FALSE at a rising edge of bExecute, the output queue poqDataOut is emptied |
|
|
bAppend |
BOOL |
FALSE |
If FALSE at a rising edge of bExecute, the output queue poqDataOut is emptied |
|
|
poqDataIn |
POINTER TO SMC_OUTQUEUE |
NULL |
This input points to the SMC_OUTQUEUE structure object, which describes the SMC_GEOINFO objects of the path; typically it points to the output poqDataOut of the preceding module (e.g. SMC_NCDecoder / SMC_SmoothPath ). |
|
|
nSizeOutQueue |
UDINT |
0 |
This variable contains the size of the data buffer, the list of SMC_GEOINFO structure objects will be written to. This buffer must be able to hold at least five SMC_GEOINFO objects. Otherwise, the function block will not execute any actions at all. Its size may be predefined, but may be modified later only during a reset. It is recommended to create the buffer as described by the example below: ExampleBuf: ARRAY[1..50] OF SMC_GEOINFO The appropriate buffer size will then be retrieved by use of the operator sizeof(ExampleBuf). |
|
|
pbyBufferOutQueue |
POINTER TO ARRAY [0..0] OF SMC_GEOINFO |
NULL |
This input must point to the first byte of the memory area that is allocated for the SMC_OUTQUEUE structure. This area must be at least as big as defined in nSizeOutQueue. Typically the allocation of the memory buffer is done in the declaration part of the IEC-program by defining an array of SMC_GEOINFO e.g. BUF: ARRAY[1..50] OF SMC_GEOINFO; for a buffer that can store 50 path elements). The value may be predefined, but may be modified later on only during a reset. |
|
|
bStrictlyHoldAccDecABC |
BOOL |
FALSE |
If TRUE, the maximal accelerations and decelerations of A, B, C are strictly held. Otherwise, we use a heuristic that may lead to quicker profiles, but occasionally violate the A/B/C-acceleration-limit, if A/B/C move quickly while there is an ac- / deceleration on the path. |
|
|
Output |
bDone |
BOOL |
FALSE |
|
|
bBusy |
BOOL |
FALSE |
TRUE, while execution of function block is not finished and the process on the path object is still running |
|
|
bError |
BOOL |
FALSE |
Signals that an error has occurred within the function block |
|
|
wErrorID |
SMC_ERROR |
SMC_NO_ERROR |
Error identification |
|
|
poqDataOut |
POINTER TO SMC_OUTQUEUE |
NULL |