TYPE SMC_ERROR :
The enumeration SMC_ERROR contains all error numbers that can be returned by SoftMotion function blocks. SMC_ErrorString generates an error string output.
InOut:
|
Name |
Initial |
Comment |
|
0 |
No error |
|
|
1 |
Communication error. For example, Sercos ring has broken. |
|
|
2 |
Axis error |
|
|
3 |
Fieldbus has lost synchronism |
|
|
10 |
Position outside of permissible range of SWLimit |
|
|
11 |
Hardware end switch is active |
|
|
12 |
This error occurs if a linear axis has more than 2^15 32-bit overflows of the position in increments |
|
|
13 |
Drive status Halt or Quickstop is not supported |
|
|
14 |
Drive has no power |
|
|
15 |
This error is no longer used |
|
|
16 |
Position lag error. Difference between set and current position exceeds the given limit |
|
|
17 |
Homing error reported by axis |
|
|
18 |
A problem with the license occurred |
|
|
20 |
Controller enable not done or brake applied |
|
|
21 |
Axis in wrong controller mode |
|
|
25 |
Invalid action at logical axis |
|
|
30 |
Motion creating module has not been called again before end of the motion |
|
|
31 |
Type of given AXIS_REF variable is not AXIS_REF |
|
|
32 |
AXIS_REF variable has been exchanged while the module was active. |
|
|
33 |
Axis disabled while being moved. MC_Power.bRegulatorOn |
|
|
34 |
Axis in its current state cannot execute a motion command, because the axis doesn't signal currently that it follows the target values. |
|
|
35 |
The drive reported an error during an ongoing movement. |
|
|
40 |
Maximum velocity fMaxVelocity exceeded |
|
|
41 |
Maximum acceleration fMaxAcceleration exceeded |
|
|
42 |
Maximum deceleration fMaxDeceleration exceeded |
|
|
50 |
Invalid velocity or acceleration values |
|
|
51 |
Mode requests for safety reasons use of end switches. |
|
|
60 |
No free handle has been sent to open file. |
|
|
70 |
Mode not supported |
|
|
71 |
In current mode, controller mode cannot be changed. |
|
|
72 |
SMC_SetControllerMode has been interrupted by MC_Stop or errorstop. |
|
|
75 |
Axis not in correct controller mode. Deprecated, no longer returned by SMC_SetTorque. |
|
|
80 |
Error at startup of the axis group |
|
|
81 |
The axis is not yet in the required state. |
|
|
85 |
The function block does not support virtual or logical axes. |
|
|
86 |
The number of absolute bits is invalid, must be in the range 8 .. 32. |
|
|
90 |
Invalid values |
|
|
91 |
Gearing parameters must not be changed as long as the drive is under control. |
|
|
92 |
Invalid modulo period (<= 0 or greater than half the bus bandwidth) |
|
|
93 |
The modulo period in increments is not an integer, but the modulo-handling is done by the drive. |
|
|
110 |
Axis contain no information on cycle time (fTaskCycle = 0). |
|
|
120 |
Axis without error |
|
|
121 |
Axis does not perform error-reset. |
|
|
122 |
Error could not be reset. |
|
|
123 |
Communication with the axis did not work. |
|
|
130 |
Parameter number unknown |
|
|
131 |
Error during transmission to the drives. See error number in function block instance ReadDriveParameter. |
|
|
132 |
No assignment for drive parameters available |
|
|
133 |
Conversion of the value to / from the drive parameters failed. Unknown SoftMotion parameters |
|
|
140 |
Parameter number unknown or writing not allowed |
|
|
141 |
See error number in function block instance WriteDriveParameter |
|
|
142 |
No assignment for drive parameters available |
|
|
143 |
Conversion of the value to / from the drive parameters failed Unknown SoftMotion parameters |
|
|
170 |
Axis has not been in standstill state. |
|
|
171 |
Error at start of homing action. |
|
|
172 |
Error at start of homing action. |
|
|
173 |
Error at stop after homing. Deceleration may not be set. |
|
|
174 |
Drive is in errorstop status. Homing cannot be executed. |
|
|
180 |
Unknown error at stop |
|
|
181 |
Invalid velocity or acceleration values |
|
|
182 |
Direction = shortest not applicable |
|
|
183 |
Drive is in errorstop status. Stop cannot be executed |
|
|
184 |
Instance of MC_Stop blocking the axis by Execute = TRUE has not been called yet. MC_Stop (Execute = FALSE) has to be called. |
|
|
185 |
Cannot interrupt an ongoing MC_Stop |
|
|
200 |
The task interval of the bus task could not be determined. |
|
|
201 |
Invalid velocity or acceleration values |
|
|
202 |
Direction error |
|
|
226 |
Invalid velocity or acceleration values |
|
|
227 |
Direction error |
|
|
251 |
Invalid velocity or acceleration values |
|
|
252 |
Direction error |
|
|
276 |
Invalid velocity or acceleration values |
|
|
277 |
Direction error |
|
|
278 |
Except from aborting, don't call a major mvt-FB after SMC_MoveSuperimposed |
|
|
300 |
No longer used; only for compatibility |
|
|
301 |
Invalid velocity or acceleration values |
|
|
302 |
Direction = shortest/fastest not applicable |
|
|
325 |
Erroneous array size |
|
|
326 |
Step time = t#0s |
|
|
350 |
Erroneous array size |
|
|
351 |
Step time = t#0s |
|
|
375 |
Erroneous array size |
|
|
376 |
Step time = t#0s |
|
|
400 |
Trigger already active |
|
|
401 |
DriveInterface does not support the window function. |
|
|
402 |
Communication error |
|
|
410 |
Trigger already de-allocated |
|
|
426 |
Invalid velocity or acceleration values |
|
|
427 |
Invalid direction |
|
|
451 |
Invalid velocity or acceleration values |
|
|
452 |
Invalid direction |
|
|
453 |
Direction = fastest not applicable |
|
|
475 |
SMC_ChangeDynamicLimits may only be called in state standstill. or power_off. |
|
|
476 |
Invalid velocity, acceleration, deceleration or jerk values |
|
|
600 |
Cam does not contain any tappets. |
|
|
601 |
Tappet group ID exceeds MAX_NUM_TAPPETS |
|
|
602 |
More than 32 accesses on one CAM_REF |
|
|
625 |
No cam selected |
|
|
626 |
Master axis out of valid range |
|
|
627 |
Velocity and acceleration values must be specified for ramp_in function |
|
|
628 |
Scaling variables fEditor/TableMasterMin/Max are not correct |
|
|
629 |
Too many tappets became active during one cycle |
|
|
640 |
Function block for the given cam format is not implemented |
|
|
675 |
RatioDenominator = 0 |
|
|
676 |
Acceleration invalid |
|
|
677 |
Deceleration invalid |
|
|
678 |
Status Enable/Disable of the master has changed without permission |
|
|
679 |
Jerk invalid |
|
|
725 |
Velocity and acceleration/deceleration values invalid |
|
|
726 |
Rotation axis with fPositionPeriod = 0 |
|
|
750 |
Type of given cam is not MC_CAM_REF. |
|
|
751 |
Master area, xStart and xEnd, from CamTable is not covered by curve data. |
|
|
752 |
Cam data table has empty master range. |
|
|
753 |
Cam data master has invalid max-, min-values. |
|
|
754 |
Cam data slave has invalid max-, min-values. |
|
|
775 |
During coupling of slave axis, master axis has changed direction of rotation. |
|
|
776 |
Input AvoidReversal is set, but slave reversal cannot be avoided. |
|
|
777 |
Input AvoidReversal must not be set for finite slave axes. |
|
|
800 |
Gear backlash fBacklash too large (> position periode/2) |
|
|
825 |
Internal error: computation of quadratic trajectory failed |
|
|
826 |
Internal error: computation of quadratic trajectory failed |
|
|
827 |
Internal error: computation of quadratic trajectory failed |
|
|
828 |
Internal error: computation of quadratic trajectory failed |
|
|
829 |
Internal error: computation of quadratic trajectory failed |
|
|
830 |
Internal error: computation of quadratic trajectory failed |
|
|
831 |
Internal error: computation of quadratic trajectory failed |
|
|
832 |
Internal error: computation of quadratic trajectory failed |
|
|
850 |
Action only permitted in standstill or power_off. |
|
|
851 |
Invalid ramp type |
|
|
852 |
Action only permitted in standstill or power_off. |
|
|
853 |
Invalid motion type or position period |
|
|
854 |
Function block only applicable to virtual axis. |
|
|
1000 |
Target is not licensed for CNC. |
|
|
1001 |
Path cannot be processed because set velocity = 0. |
|
|
1002 |
Last object of path has end velocity <> 0. |
|
|
1003 |
Warning: GEOINFO-List processed in DataIn but end of list not reached. Reason:
|
|
|
1004 |
Velocity at Stop > 0 |
|
|
1005 |
Too much SMC_Interpolator recursions. SoftMotion error |
|
|
1006 |
SMC_CheckVelocities is not the last processed function block, that accesses to the OutQueue-data by poqDataIn. |
|
|
1007 |
Internal or numeric error |
|
|
1008 |
Velocity and acceleration / deceleration is null or to low |
|
|
1009 |
FB called with dwIpoTime = 0 |
|
|
1010 |
Jerk invalid because jerk must be positive |
|
|
1011 |
Internal error. Calculation algorithm incorrectly |
|
|
1012 |
Invalid velocity mode |
|
|
1013 |
More than the allowed number of axes has been interpolated. |
|
|
1014 |
The segment is numerically degenerate: It is very short and at the end of the queue. It should be ignored. |
|
|
1050 |
Warning: poqDataIn of OutQueue is created too small. Adherence of stops not guaranteed. |
|
|
1051 |
Path does not go completely in queue. |
|
|
1070 |
Direction input has an invalid value. |
|
|
1071 |
Could not determine position on CNC path for the given x-position. |
|
|
1080 |
Warning: poqDataIn of OutQueue is created too small. Adherence of stops not guaranteed |
|
|
1081 |
Warning: Final velocities inconsistent |
|
|
1100 |
Velocity and acceleration/deceleration values non-positive |
|
|
1120 |
Values of fGapVelocity / fGapAcceleration / fGapDeceleration non-positive |
|
|
1200 |
Acceleration value impermissible |
|
|
1201 |
Deceleration value impermissible |
|
|
1202 |
Data underrun. Queue has been read and is empty. |
|
|
1203 |
Jump to line cannot be executed because line number is unknown. |
|
|
1204 |
Syntax invalid |
|
|
1205 |
Objects are not supported in 3D mode. |
|
|
1206 |
Negative value as a period of additional axes invalid |
|
|
1207 |
Not both axes A and U are interpolated. PA and PU are mutually exclusive. |
|
|
1208 |
Not both axes B and V are interpolated. PB and PV are mutually exclusive. |
|
|
1209 |
Not both axes C and W are interpolated. PC and PW are mutually exclusive. |
|
|
1210 |
For G54/G55/G56, either all of A,B,C or none must be given if orientation mode is not equal to SMC_ORI_CONVENTION.ADDAXES. |
|
|
1211 |
The z-axis of the decoder CS must be equal to the z-axis of the machine CS. |
|
|
1212 |
Scaling would distort commanded circle or ellipse. |
|
|
1213 |
New relative rotation of the DCS (G55) would affect the scaling |
|
|
1214 |
For G54/G55/G56, either all of I,J,K or none must be given. |
|
|
1300 |
Buffer too small |
|
|
1301 |
Buffer elements have wrong type. |
|
|
1302 |
Current line of the Interpolator could not be found. |
|
|
1400 |
Internal error in CNC |
|
|
1410 |
G75 not allowed during tool radius correction |
|
|
1411 |
Queue full, but no further cartesian element |
|
|
1412 |
Tool radius correction does not support movement type SPLINE3D_5 |
|
|
1500 |
Given CNC program is not of type SMC_CNC_REF |
|
|
1501 |
Given OutQueue is not of type SMC_OUTQUEUE |
|
|
1502 |
4-byte aligned buffer part is not used in pbyBuffer |
|
|
1600 |
Function block only works with 2D paths. |
|
|
1700 |
Range for smoothing too large |
|
|
1701 |
Invalid input dSmoothingPart ]0..1] |
|
|
1800 |
SMC_SegmentAnalyzer detects that OutQueue buffer is full but not completed. The function block can only operate when OutQueue fits the buffer completely. |
|
|
1801 |
OutQueue buffer changed while the function block is operating on them. |
|
|
1820 |
Invalid input value in dSplittingParameter |
|
|
1830 |
Position cannot be saved. Interpolator is inactive |
|
|
1831 |
Saved position has not been found so far. It is probably on a different path. |
|
|
1832 |
Structure passed in ePos contains no saved position. SMC_BlockSearchSavePos is not executed or in a wrong way. |
|
|
1900 |
Feature flag must be in the range {1, .., 31}. |
|
|
1901 |
Function block does not support h-functions. |
|
|
1902 |
Function block only works in 3D-Mode. |
|
|
1903 |
Internal error computing the spline. |
|
|
1910 |
wAdditionalParameter is too big |
|
|
1950 |
The value of one of the inputs is invalid. |
|
|
2000 |
File does not exist |
|
|
2001 |
No buffer allocated |
|
|
2002 |
Buffer too small |
|
|
2003 |
Data underrun. Buffer has been read, is empty. |
|
|
2004 |
Placeholder variable could not be replaced. |
|
|
2005 |
Input pvl does not point to a SMC_VARLIST object. |
|
|
2006 |
Input pStringBuffer is not used or does not point to a variable of type SMC_StringBuffer |
|
|
2007 |
In the CNC program more different strings are used as reserved in pStringBuffer. |
|
|
2050 |
File could not be opened. |
|
|
2051 |
No buffer defined |
|
|
2052 |
Buffer too small |
|
|
2053 |
Unexpected end of file |
|
|
2100 |
File could not be opened |
|
|
2101 |
Buffer overrun. WriteToFile must be called more frequently. |
|
|
2200 |
File could not be opened. |
|
|
2201 |
Saved cam too big |
|
|
2202 |
Wrong compilation mode |
|
|
2203 |
File has wrong version |
|
|
2204 |
Unexpected end of file |
|
|
3001 |
||
|
3002 |
File could not be created. |
|
|
3003 |
Error at reading the parameters. |
|
|
3004 |
Timeout during preparing the parameter list. |
|
|
5000 |
Nominator of the conversion factor dwRatioTechUnitsDenom of the Encoder reference is 0 |
|
|
5001 |
Other module trying to process motion on the Encoder axis |
|
|
5002 |
Filter depth is invalid |
|
|
10000 |
Buffer pBuffer too small |
|
|
10001 |
The function block must be applied to a path that fits completely in the buffer. |
|
|
11000 |
The axis group is in the wrong state for the requested operation. |
|
|
11001 |
More than the maximum allowed number of axes has been added to an axis group. |
|
|
11002 |
The dynamic limits of a single axis are invalid. (fSWMaxVelocity/Acceleration/Deceleration/Jerk) |
|
|
11004 |
The given coordinate system is invalid for the requested operation |
|
|
11005 |
An axis of the axis group is in state error |
|
|
11006 |
The given buffer mode is not supported |
|
|
11007 |
The dynamic factor is not in the range ]0 .. 1] |
|
|
11008 |
The dynamic limits for the movement are invalid. |
|
|
11009 |
The given axis is not part of the axis group. |
|
|
11010 |
The requested operation is not supported |
|
|
11011 |
No kinematic configuration has been configured. |
|
|
11012 |
The number of axes is not equal to the number of axes needed by the kinematic transformation |
|
|
11013 |
A coordinated movement has been interrupted by a single axis movement. |
|
|
11014 |
An error occurred while following the computed set values. |
|
|
11015 |
An axis group cannot depend on more than one master axis group. |
|
|
11016 |
An axis group A may not depend on another axis group that depends on A. |
|
|
11017 |
A dependant axis group must be executed in the same task. |
|
|
11018 |
An axis belonging to an axis group must be executed in the same task. |
|
|
11019 |
A second activation of the function block occurred while the PCS was still used by buffered motion commands. |
|
|
11020 |
An error ocurred in a previous motion command. |
|
|
11021 |
A parameter of an administrative function block is invalid. |
|
|
11022 |
One of the axes of the group uses an unsupported ramp type. Only trapez and quadratic are supported. |
|
|
11023 |
invalid transition parameter |
|
|
11024 |
Internal error in the state machine of the axis group. |
|
|
11025 |
CP-Tracking: Cannot keep the path; try to reduce the dynamics on the path and / or the dynamics when entering CP-Tracking. |
|
|
11026 |
current position does not allow continuation. |
|
|
11027 |
Buffer in continueData is too small; big external movement-queue-buffer in use. |
|
|
11028 |
The checksum stored in the continue data is wrong. The continue data either was not written by MC_GroupInterrupt, or was modified afterwards. |
|
|
11100 |
Internal error in the kernel |
|
|
11101 |
Task cycle time not positive |
|
|
12000 |
Invalid parameters |
|
|
12001 |
The input constellation (typ. cartesian values) are incompatible with the configuration. Typically this means that the given position is outside of the working area of the kinematic transformation. |
|
|
12002 |
The tool cannot work together with the positioning-part of the machine. Either, the positioning-part doesn't implement ISMPositionKinematics2, or the tool cannot deal with the positioning's image of orientations. |
|
|
12003 |
The FB implements |ISMKinematicWithInitialization|, but hasn't been Initialized yet. |
|
|
12100 |
The cache of the CP planner is too small. |
|
|
12101 |
The evaluation of the position on a geometric element failed. |
|
|
12102 |
Non-continuable state reached (internal error). |
|
|
12103 |
Maximum trajectory length exceeded (internal error). |
|
|
12104 |
Path acceleration too high (invalid state, internal error). |
|
|
12105 |
Maximum number of iterations exceeded (internal error). |
|
|
12106 |
No trajectory could be computed (internal error). |
|
|
12107 |
The out-queue is full (internal error). |
|
|
12108 |
Queue underrun: no element left in queue. |
|
|
12109 |
Invalid queue (invalid size or pointer) |
|
|
12110 |
An internal error occurred while blending two CP movements |
|
|
12111 |
The three points that define the circle are collinear. |
|
|
12112 |
The center point is not on the perpendicular bisector of the start and end point. |
|
|
12113 |
The radius is zero |
|
|
12114 |
The distance between start and end point is larger than the diameter. (When trying to create a circle using SMC_Circ_Mode.Radius.) |
|
|
12115 |
The start and end point are equal (SMC_Circ_Mode.Radius). |
|
|
12116 |
The blending spline is degenerate (too short or non-regular) |
|
|
12117 |
The path element cannot be created because it is too short. |
|
|
12118 |
The path could not be cut for aborting movement (internal error). |
|
|
12119 |
The given angular velocity or acceleration is invalid (quaternion with non-zero real part, internal error). |
|
|
12120 |
The given orientation is invalid (non-orthonormal matrix or non-unit quaternion, internal error). |
|
|
12121 |
The given time budget for the computation is exceeded (internal error). |
|
|
12122 |
A limit of an axis has been violated. This can happen if a CP movement is done too close to a singularity or if the path has a very high curvature. |
|
|
12123 |
The kinematic configuration of the start position differs from the current configuration. The CP movement would pass a singularity. |
|
|
12124 |
The kinematic configuration of the end position differs from the current configuration. The CP movement would pass a singularity. |
|
|
12125 |
The kinematic configuration of the start position differs from the end position. The CP movement would pass a singularity. |
|
|
12126 |
If a CP-halt/-stop is commanded, some information has to be transferred to the bus task. We except this to happen before the next cycle of the slow task. |
|
|
12127 |
The stop trajectory could not be found in the interval. (internal error) |
|
|
12128 |
The kinematics does not support the orientation mode "Axis" for continuous path movements. |
|
|
12129 |
The axis orientation interpolation mode is not supported for CP movements with a dynamic PCS (tracking). |
|
|
12130 |
An invalid path element has been created (internal error) |
|
|
12131 |
The transition between two path elements is not G2 continuous, and there is no stop (internal error) |
|
|
12132 |
Axis orientation interpolation mode is used, but between the start end end position, there is a singularity of the position kinematics. |
|
|
12133 |
The position kinematics has configurations but does not implement the interface ISMPositionKinematics_Offset2. In this case, axis orientation interpolation is not possible. |
|
|
12134 |
The target position of a rotary axis will not be reached in the commanded period. (E.g. the commanded target position is -170°, but the target will be reached with position 190° instead.) This means that the chosen interpolation to the target position is not compatible with the commanded position. |
|
|
12135 |
A rotary axis has violated the allowed axis range during a CP movement. The CP movment is not in the working area. |